BoonHauler wrote:I would agree on your interpretation. How would Rogue know where or how their CC's were going to be installed so probably err on the side of caution.
Here's what the manual states:Rogue Manual wrote:
11.3 Grounding
The enclosure of the MPT-3048 is floating with respect to all circuit voltages and may be used with either negatively or positively grounded systems. It may also be used with systems in which neither negative nor positive are grounded, as allowed by NEC 690-41 for systems of less than 50 volts. Most systems are negatively grounded, or utilize an isolated ground to which neither negative nor positive conductors are grounded.
F Do not ground any positive or negative conductor within the enclosure of the MPT-3048. Always do so at a common location in the DC load center, and through a Ground Fault Protection Device (GFPD), to comply with NEC requirements. The equipment grounding conductor attached to the MPT-3048’s grounding lug should be an insulated wire with a minimum size of 10 gauge copper.
! The voltage between ground and the positive and negative connections to the controller must never exceed 100 volts.
For code compliance, basic electrical safety, and enhanced EMI shielding, one copper ground wire must be securely fastened to the enclosure. A lug and bolt are included with the unit and may be fastened to the 1/4” threaded hole in left side of the unit (Figure 11.3.1). The other end of the ground wire is connected to the grounded bus bar within your load center.
So, after all that I take it as a standard #10 ground wire from the CC enclosure to a Ground Buss, this states D/C Load Center meaning a ground buss in the panel enclosure. The assumption is that the "D/C Load Center" ground has been 'earthened' or connected to a ground rod.
Now how many of you out there connects your R/V's electrical systems "ground buss", if you even have one, to a ground rod, with a #6 wire between the rod and the buss?
Like I said, this is stick & brick code language.
May-11-2014 12:16 AM
May-10-2014 10:10 PM
Rogue Manual wrote:
11.3 Grounding
May-10-2014 08:55 PM
May-10-2014 08:09 PM
May-10-2014 05:39 PM
brulaz wrote:
there's other MPPT controllers out there are cheaper and probably would have been good enough. But I'm a sucker for quality electronics, especially when they're designed and made in the Oregon woods.
May-10-2014 04:55 PM
pianotuna wrote:
Hi,
I'd be most interested to know what panels you chose to go with the Rogue!
May-10-2014 10:06 AM
May-10-2014 09:45 AM
May-10-2014 09:21 AM
brulaz wrote:BoonHauler wrote:brulaz wrote:
Rogue says to run a separate 10ga from the MPPT grd terminal to "a common location in the DC load center, and through a Ground Fault Protection Device (GFPD), to comply with NEC requirements".
What sort of GFPD are people using if anything? Could I just connect the grd to the neg wire in the load center? Or should i just ignore the Mppt grd terminal?
What model controller do you have? I'd like to see what context they're refering to.
As for Ground Fault Breakers, here's a Link
Here's what that link says for the MNDC-GFP63:
"The 2011 NEC requires a GFP now on all systems. It used to be that they were required only when PV panels were installed on the roof of a dwelling. Now even if you Solarize your doghouse, a ground fault protector is required in order to pass inspection."
Sort of agrees with the quote from Rogue above. It's a Rogue 3048.
I presume you would put this between the mppt grd and the frame? Maybe if I ever place another order to NAWS I'll get one.
EDIT: Maybe not.
They seem to be high amperage 63A,80A and designed for grnd faults between grounded solar panels and battery neg. Half the MNDC-GFP63 is a 63A breaker between the solar panel + and the mppt + in (with another regular 63A breaker in series) and the other half breaker of the MNDC-GFP63 is from the solar panel grnd to battery neg.
My system is only 15A max with un-grounded solar panels.
May-10-2014 04:31 AM
May-10-2014 04:24 AM
May-10-2014 02:21 AM