pianotuna wrote:
Set up a proper transfer switch. I had a nice six circuit manual one in my home. It was quite handy.
Oct-18-2017 02:32 PM
Oct-18-2017 02:28 PM
It takes many thousandths less power to electrocute someone than it does to trip a breaker.........
Oct-18-2017 12:48 PM
DrewE wrote:
What you say about surges doesn't make any sense to me.
Oct-17-2017 11:29 PM
Oct-17-2017 11:27 PM
Oct-17-2017 07:55 PM
Oct-17-2017 06:52 PM
Oct-17-2017 06:49 PM
JaxDad wrote:
No, it does NOT do the same thing.
The ground and the neutral are bonded in the breaker panel and meter base. Backfeeding the house without breaking that bond means there is potential in the neutral wire beyond the meter base and back out into the grid.
A typical breaker doesn’t kick over with enough force to trip a second breaker, add to that the fact that it requires a massive overload to trip a breaker on a short circuit condition, not just a simple overload, like 5 times the normal load to trip.
If you haven’t transferrred the neutral, that massive overload could, and likely will, pass through the meter base and out into the grid.
Oct-17-2017 06:04 PM
Oct-17-2017 05:09 PM
Oct-17-2017 04:33 PM
Dutch_12078 wrote:Dusty R wrote:JaxDad wrote:cgmartine wrote:
The third option, the breaker interlock, is exactly what I pictured in my mind. I believe I could do it myself, but just to be extra safe, I will hire an electrician to do it for me.
I’d be surprised if you could get an electrician to do that sort of a job. It’s not legal because it’s potentially very dangerous.
Please do it properly and install a transfer switch.
A breaker interlock does the same thing as a transfer switch, and is legal.
Exactly... The interlock doesn't allow the generator supply breaker to be turned on until the main line breaker is turned off, and vice versa.
Oct-17-2017 11:41 AM
Oct-17-2017 10:26 AM
Oct-17-2017 09:44 AM
ktmrfs wrote:owenssailor wrote:SAR Tracker wrote:
Here in Central Oregon, we have "emergencies" once in a while.
I really hope you shut off the main beaker to your house when you do a jury rigged approach like this. Otherwise you can send 120V power out to the lines where people are working. This could hurt or kill them!!!!!!!!
ah..... what the OP described is safe. by using a power strip NOTHING is connected to the house electrical system. He's NOT using any inside outlets connected to the panel.