Splitshaft wrote:
,
You plug in with a good, but not so shiny and or clean 30-amp RV plug or worse yet, one that has copper oxidation already coating its blades. Yes, the copper color, not brass color you see on 30-amp blades is copper oxidation from previous overheating and results in extra electrical resistance. Clean it off or risk a meltdown.
โOct-25-2019 04:01 PM
myredracer wrote:Yes and there is also a provision in the code that relates to continuous draw circuits. Code requires a supply 125% of the rated load in this circumstance. (load 80% of supply is mathematically the same). Continuous load is defined as 3+ hours.philh wrote:Not sure if you're being sarcastic or serious. Technically and by code you should be able to draw 30 amps indefinitely.
why would pulling 30a on a circuit rated for 30a be a problem?
โOct-25-2019 03:40 PM
โJun-02-2019 01:55 PM
โMay-31-2019 06:12 PM
โMay-31-2019 10:35 AM
โMay-28-2019 05:23 PM
โMay-28-2019 02:41 PM
โMay-28-2019 12:49 PM
Cummins12V98 wrote:A 12.5K AC unit has a full load draw of 12.5 - 13.1 amps so 2 ACs is already at 25 - 26 amps. The converter is going to be drawing at least a few amps and you can't turn it off, so you're pretty close to or even at 30 amps. If you're running the fridge on electric, that's another 2.5 amps which will put you over 30 amps. Turn on any other loads, high draw or not and you are def. over 30 amps.
The idea is to turn off all high draw items and the two AC's on 30A will be fine. Yes low voltage could be an issue! There are variables in all situations. The 30A plug should be of good quality and it's receptacle on the pedestal.
โMay-28-2019 12:37 PM
philh wrote:Not sure if you're being sarcastic or serious. Technically and by code you should be able to draw 30 amps indefinitely. But the receptacles in pedestals, especially 30 amps, are often in poor shape with either loose contacts or dirty/corroded contacts or both. And many times, RV-ers don't look after their shore power cords and the plug blades can also be dirty/corroded. A sloppy connection and dirty contact surfaces creates enough resistance to cause overheating and a meltdown which is not uncommon. Lots of pics are on the 'net.
why would pulling 30a on a circuit rated for 30a be a problem?
โMay-28-2019 09:39 AM
myredracer wrote:
Drawing high amps (on 30 amp pedestal) for extended periods can result in an overheated plug to pedestal connection. There are even some that say you should never draw over 80% of 30 amps, 24 amps (which I disagree with). Two AC units (rated @ 12.5 FLA) is already at 25 amps and that's *if* the voltage is near or at 120 volts. Add in the converter draw, fridge on electric, TV and you're over 30 amps.
To size a "main" breaker by code calculation, if you have AC units rated at say 12.5 FLA and were drawing 5 amps from the converter and no other loads, you would require 12.5 amps + 5 amps + 20 amps (required breaker size for startup), you would need a breaker rated for min. 37.5 amps. You would then need to go to the next available size up, or 40 amps.
Doesn't matter *if* it seems like two AC units are working fine, it IS causing damage to the motor windings which degrades the insulation over time and shortens the life of AC units. The voltage at the AC terminals will be somewhat less too.
โMay-28-2019 09:36 AM
pianotuna wrote:
From your own figures 3 x 13 = 39 amps = not able to run all 3 on 30 amps.Cummins12V98 wrote:
I how have 3 AC's and use them ALL. If I were to be at a 30A park I would do the same.
This is what my 15k AC draws once it starts pulling power.
There was already 1A draw on L1 before I turned on the AC.