โJul-03-2018 03:42 PM
โJul-06-2018 08:21 AM
โJul-06-2018 06:37 AM
pnichols wrote:Larger wire with less voltage loss is used for a 50A pedestal so you are more likely to have higher voltage with a 30A rig.
I'm curious. If one has a 30A RV, but pays for a 50A RV site and then uses a 50A-to-30A adapter on the 50A pedestal receptacle to power their rig ... do they still run the risk of experiencing 30A low voltage service on high usage days?
โJul-06-2018 03:05 AM
Lynnmor wrote:pnichols wrote:
I'm curious. If one has a 30A RV, but pays for a 50A RV site and then uses a 50A-to-30A adapter on the 50A pedestal receptacle to power their rig ... do they still run the risk of experiencing 30A low voltage service on high usage days?
Of course. It is possible that the 50 amp site might have less voltage drop if the wire size is larger, but you have no way of knowing that till you try both the 30 and 50 sites under load.
I started this thread to point out a significant problem. If the voltage is too low coming into the campground it can only get worse at the connection.
โJul-06-2018 02:02 AM
pnichols wrote:
I'm curious. If one has a 30A RV, but pays for a 50A RV site and then uses a 50A-to-30A adapter on the 50A pedestal receptacle to power their rig ... do they still run the risk of experiencing 30A low voltage service on high usage days?
โJul-05-2018 11:04 PM
โJul-05-2018 10:56 PM
โJul-05-2018 10:02 AM
pianotuna wrote:
My comfort zone is 107 and up, so the current ems units are useless to me.
SoundGuy wrote:
Your choice, but clearly Progressive Industries' engineers who have selected 104 vac as their low voltage threshold would disagree. Choices, choices - whom to believe? :W
myredracer wrote:
You might start with reading the RV AC manufacturer's min. requirements. I've seen one of them specify. min. 105.
myredracer wrote:
As well, a static min. voltage reading isn't always the whole picture because when an AC starts up and draws 5-6 times running current, voltage can drop out of sight and lead to damage to the motor windings over time.
โJul-05-2018 09:30 AM
myredracer wrote:SoundGuy wrote:You might start with reading the RV AC manufacturer's min. requirements. I've seen one of them specify. min. 105.pianotuna wrote:
My comfort zone is 107 and up, so the current ems units are useless to me.
Your choice, but clearly Progressive Industries' engineers who have selected 104 vac as their low voltage threshold would disagree. Choices, choices - whom to believe? :W
As well, a static min. voltage reading isn't always the whole picture because when an AC starts up and draws 5-6 times running current, voltage can drop out of sight and lead to damage to the motor windings over time.
โJul-05-2018 09:00 AM
SoundGuy wrote:You might start with reading the RV AC manufacturer's min. requirements. I've seen one of them specify. min. 105.pianotuna wrote:
My comfort zone is 107 and up, so the current ems units are useless to me.
Your choice, but clearly Progressive Industries' engineers who have selected 104 vac as their low voltage threshold would disagree. Choices, choices - whom to believe? :W
โJul-05-2018 08:57 AM
pianotuna wrote:
My comfort zone is 107 and up, so the current ems units are useless to me.
โJul-05-2018 08:54 AM
โJul-05-2018 08:41 AM
myredracer wrote:
During peak demands of the summer and high AC use, voltage is just gonna go down. Guaranteed. Reducing voltage drop would be an extremely expensive proposition and will never happen.
โJul-05-2018 08:12 AM
Lwiddis wrote:
โthey said nothing can be done.โ
Yes it can fixed. โTheyโ just donโt want to spend the money. To heck with your RV damage.
โJul-04-2018 10:24 AM