vermilye wrote:
Then there is the 120V Delta. We had one in one of our older theaters. "Shocks" new electricians the first time they meter one. 120V between everything...
โJan-29-2019 10:18 AM
โJan-29-2019 07:39 AM
โJan-18-2019 04:26 AM
23hotrodr wrote:Bill.Satellite wrote:
We discussed the install and the installer was very familiar with an RV plug. I had just never seen the 208 setup and was looking for confirmation that using that was not a problem since I never use anything other than 120.
Since you have confirmed the electrician will properly wire the receptacle--
208 3 phase will yield the following in your situation--
208 volts across 2 hot leads
115 volts from each hot to neutral
This will work perfectly fine. You can and should confirm it with a volt meter. Good luck-- Mick
โJan-18-2019 02:55 AM
Bill.Satellite wrote:
We discussed the install and the installer was very familiar with an RV plug. I had just never seen the 208 setup and was looking for confirmation that using that was not a problem since I never use anything other than 120.
โJan-17-2019 01:45 PM
โJan-17-2019 06:28 AM
โJan-17-2019 06:10 AM
Bill.Satellite wrote:
Not sure why anyone thought I was going to try to install this myself, but I have 2 professionals installing the plug but not all professionals understand exactly what is required of RV's. They know what an RV plug is and the wiring required. I just wanted a little reassurance that they understood what I hoped they understood and it appears that they do. Hopefully, they will get the work done this week or next and I will be plugged in 30 seconds from the office!
โJan-16-2019 07:29 PM
CA Traveler wrote:DrewE wrote:Sine waves for sure. But a 240V motor sees that the combined voltage and amps are 120 degrees out of phase with each other. So definitely no longer 240V single phase.
Although the two phases are 120 degrees from each other, the phase to phase waveform still works out to be a sine wave, so it's "normal" single phase power albeit at a lower voltage. There are plenty of single-phase motors that are rated to operate at either 208V or 240V (and likewise plenty that are not so rated).
As long as the motor and it's load is designed for both power sources then all is good. Appreciate the input.
โJan-16-2019 06:24 PM
CA Traveler wrote:DrewE wrote:Sine waves for sure. But a 240V motor sees that the combined voltage and amps are 120 degrees out of phase with each other. So definitely no longer 240V single phase.
Although the two phases are 120 degrees from each other, the phase to phase waveform still works out to be a sine wave, so it's "normal" single phase power albeit at a lower voltage. There are plenty of single-phase motors that are rated to operate at either 208V or 240V (and likewise plenty that are not so rated).
As long as the motor and it's load is designed for both power sources then all is good. Appreciate the input.
โJan-16-2019 06:08 PM
ScottG wrote:Interesting question.Cummins12V98 wrote:
HMMMMM, I have a 220V Washer AND Dryer. I also have 220V Cheap Heat.
I'm curious, what happens if you turn on your washer, drier or CH when plugged into 30A (120)?
Or do they just expect us to be smarter than that.. ๐
โJan-16-2019 05:59 PM
ScottG wrote:Cummins12V98 wrote:
HMMMMM, I have a 220V Washer AND Dryer. I also have 220V Cheap Heat.
I'm curious, what happens if you turn on your washer, drier or CH when plugged into 30A (120)?
Or do they just expect us to be smarter than that.. ๐
โJan-16-2019 05:48 PM
DrewE wrote:Sine waves for sure. But a 240V motor sees that the combined voltage and amps are 120 degrees out of phase with each other. So definitely no longer 240V single phase.
Although the two phases are 120 degrees from each other, the phase to phase waveform still works out to be a sine wave, so it's "normal" single phase power albeit at a lower voltage. There are plenty of single-phase motors that are rated to operate at either 208V or 240V (and likewise plenty that are not so rated).