SJ-Chris wrote:
I have received and bench tested the thermostat I purchased for this mod so that I know how it works. Haven't played with the bonus app yet, but that should be fun.
https://www.amazon.com/Temperature-Controller-99%C2%B0C-999%C2%B0C-One-Channel-Thermocouple/dp/B09TT7VWCK
Pretty straightforward once I figured things out. This thermostat operates a relay. I will ultimately run the 12v power going to the refrigerator control board from the "on/off" button control inside the RV through the relay. This should cover either AC or propane operation (they both require the 12v supply to the refrigerator control board). That same 12v line will supply power to this thermostat device, so it will only be on when the refrigerator is on (no power draw while in storage).
I can set a high "turn off" temperature and will likely have that at 200*C (392*F) (assuming that "normal/level" steady boiler temperature is ~180*C (356*F)...I will test this once it is installed). My understanding is the primary goal of this, or similar, device is to simply keep the internal water in the cooling unit from boiling (220-225*C...428*F-437*F...and higher). (side note: If you are wondering WHY the water boiling point is so high inside the cooling unit it is because the system is under a lot of pressure during operation.) If the boiler hits 200*C (perhaps by being out of level), the 12v power to the refrigerator will be killed (which will be sort of equivalent to turning the refrigerator off at the main "on/off" button) until the temperature drops down to some set point and then it will turn back on automatically (nice...this is what we want). I'm not sure what temp I should set this drop down temperature to. Any thoughts?
If it turns off at 200*C, do I want it turning back on once it drops down to 180*C? 150*C? 70*C? Unless someone explains otherwise, I think I'll have it turn back on once the boiler cools down to 170*C (338*F). That would be a 30*C cooling off period (from 200*C) which I'm guessing would take 10-20 minutes (??? I'll try to do a test to find out once I install it). Then the refrigerator would turn on again and try again. If the conditions were still present that was causing it to start overheating in the first place (ie. being too far out of level), then the boiler temperature would slowly rise up to 200*C and then bounce back and forth between 200*C and 170*C. Any harm in this??
Or would it be better to have the boiler temperature bounce between 200*C and 180*C such that refrigerator interior cooling can hopefully still be taking place and the interior of the refrigerator can get to its desired temps and then the regular refrigerator controls would shut down the refrigerator until it needs to cycle on again naturally?
I'm guessing it probably doesn't matter too much if the "turn back on" temperature is 180*C, 170*C, 150*C, etc. The main purpose/function is to simply limit the overheating such that it never gets above 220*C (428*F). I'm still pretty stunned to know that Norcold and Dometic find it okay to let the boiler temp get all the way up to 750-800*F before their kill fuse blows (at which time, correct me if I am wrong, the fuse will need to be physically replaced before your refrigerator will work again). With my ~$25 mod it will cut the power if it gets just 36*F above normal operating temps and then turn itself back on once the boiler temp gets back down to normal.
Above, otrfun posted their refrigerator boiler temp data from a 2 year period where they made no efforts to keep their fridge level during operation. It rose above their normal boiler temp range a max of 7-12*C (21*F max) so it seems like in general these boilers hold a pretty constant max temperature. (Thanks for the data otrfun!)
I have some family in town for Christmas so the install will likely have to wait until early January.
-Chris
โDec-17-2022 01:23 PM
โNov-23-2022 12:26 PM
SJ-Chris wrote:Vintage465 wrote:
I guess today I'm going to "be that guy"........I grew in a family that owned an RV sales and repair shop.....in the days that if you ran your fridge out of level(propane or electric)it would lockup in 20 minutes. The law was "not level, don't light". The repair was to remove the fridge turn it on it's head for 24 hours, reinstall and fire it up...level of course. 99% of the time it fixed it. So my question is, why hypothetically set your self up to do damage to your fridge when it just needs to be level. Yes I get it that driveways and streets aren't level, but.........I'll stick by "not level, don't light".
Your suggestion is fair enough...
I'm curious...Do refrigerators still "lock up" due to running out of level? Or is that a thing of the past?
I've heard about the "turn your fridge upside down" trick to "reset" the fluids (I guess?). Better than buying a new refrigerator if it fixes the problem, but somewhat painful to have to remove the refrigerator to stand it upside-down.
To answer your question...I personally try to remember not to have the refrigerator on if I'm parked significantly off-level (more than 3 degrees side to side or 6 degrees front to back). But I could always forget. More importantly, I let others use my RVs. When I do, I give them a tour inside and out showing them how everything works. It's a lot of info to communicate how every feature/etc on an RV works. It is likely that when I tell them "don't run the refrigerator if you are out of level" it goes in one ear and out the other.
So ultimately, if I want to guarantee the refrigerator doesn't run and overheat (and cause damage) when it is out of level, I can DIY a $25 fix with a high temp thermostat to shut it off. In a sense, it just automates/forces the shut off process if out of level to a point of causing damage so that I or others never need to "remember" not to run it off-level.
At the end of the day, adding a Fridge Defend or $25 DIY thermostat IS a risk reduction activity. It WILL eliminate the overheating of the boiler which WILL reduce potential damage over time and reduce the chances of a fire. Everyone gets to make their own decision on whether that risk is tiny, small, medium, high, or extreme. In my mind, if this overheating issue was ONLY about potential damage to the cooling unit over time that could cause premature death of the cooling unit and nothing else, it probably wouldn't bother me as much. But it makes me uncomfortable that something could overheat up to as much as 750*F-800*F and ultimately cause a fire in the RV (worst case scenario). If I can eliminate that risk for $25, to me it is worth it.
Happy Camping!
Chris
โNov-18-2022 05:06 PM
dougrainer wrote:
Once you have ANY blockage small or large or complete, Burping the refer(removing and standing on its side or top for 24 hours and then reinstalling,DOES NOT FIX THE CONDITION. It will allow some cooling a little better than before burping, but the problem is still there and after a few days/weeks the original blockage problem will diminish cooling. As I stated, the blockage is as hard as a weld and the cooling unit tube at the top must be cut off and a new upper tube welded in place and then recharge. Doug
โNov-18-2022 05:02 PM
JBarca wrote:
Hi Chris, some comments inserted below.
I "was" use to be like you, "thinking" the inside fridge compartment fans were totally separate from the outside fans. I have been using a battery operated Camco inside fridge compartment fan for a long time thinking it was a good thing to do, help keep the air inside all stirred up. Right?
well... I never really thought about the whole situation with an absorption fridge. My brain was still thinking like a compressor driven fridge. Freon compressor systems pump cold air into the fridge compartment. Mixing that air up make senses plus the whole fridge is made to circulate air better inside then a RV style fridge that is packed to the gills most of the time.
The absorption fridge removes heat, and what is left is cold. Right?
Then there are those laws of physics that I keep forgetting some times... hot air rises! Now think of this inside the absorption fridge, the coil fins at the top of the inside fridge compartment are removing heat. The top of the fridge compartment area is where the thermistor sensor is located that cycles the cooling unit. We really only want the hot air up at the coils, we do not need cold air up there when the cooling unit is operating, we only want the inside hot air up at the inside fins/colis.
The air in the bottom of the fridge is colder since the hotter air is rising or already up top. This happens naturally for free. When I put my Camco battery operated fan in the fridge that runs constantly, in time it mixes up all the cold air and the hot air in the fridge. It is disturbing the natural, hot air rises natural process. And the thermistor is then negatively affected by the cold air being circulated around. Yes, in "time" and if no one opens the door, the whole fridge in time comes to equilibrium until the door opens again and new warmer food is put in. But how many times did the boiler have to run to accomplish this?
Once I thought through what is happening inside the fridge, the "ah ha!" moment came to me. You really do not want to stir up all the air inside the fridge, all the time. Just like the outside fans up in the roof vent, you only need the outside fans to run when the boiler is heating. This was simple to see on the outside fans as I wanted to save battery power for boondocking and have longer fan life not running when they did not have to. There is no real value running the outside fans when the boiler is off. The same thing applies to the inside fans if you are only using them to help stop frost/ice from building up on the fins inside the fridge compartment. Thus, inside fans and outside fans should run off the same signal if you decide to add inside defrost fans.
Here is the shorter version at ARP, https://www.arprv.com/rv-fix-fridge-circulation-fan.php
Does that help explain a change in thinking?
Think about this thought, while you did camp down to approx 30F and your fridge appeared inside to be working OK, you really never know if it went into and out of, periods of the boiler is too hot or not. Some small damage may have happened and one would never know. Being below freezing temps, even at 28F etc, and the wind blowing against the side of the fridge vents, changes the amount of excess heat off the boiler. This may well have been going on with my fridge also.
Here in Ohio, we camp all year round. Granted not a lot of winter below freezing at night camping, but spring through fall is very common. Cold snaps overnight in the spring and late fall below freezing exist regularly. How many times did the boiler cycle over night? Who knows, but now we realize what can happen when boiler temps go out range and damage starts to creep in.
You have a good thread here bringing all this up.
John
PS, You have 3 campers, I have 5 of them... Don't we all need a few spares? :B We have our main camper we use all the time shown in my sig, and 4 older, very wet project campers. One of the project campers is fully restored, one is partly restored and the other two are in many pieces drying out waiting to get restored. I also seem to have many friends needing water damage repair, some small damage, others are full restores. I have just completed my 16th water damaged camper repair. I'm either nuts or like doing this extremely time consuming restoring process. Winter is coming and I'm hoping I can get back onto one of my project campers.
โNov-18-2022 11:36 AM
โNov-18-2022 07:48 AM
SJ-Chris wrote:
Snip...JBarca wrote:
Since I already have a fan up on the roof vent and a thermal disk switch to turn it on and off, I may switch the roof vent fan to the Fridge Defend. You just parallel the inside defrost fans with the roof vent fans. The ARP fan relay is rated at 20 amps, plenty for the milli amp fans I use, and the ARP defrost fans.
I'm not sure why you would want to tie your roof vent fan to your inside defrost fans. They aren't related in function. The Fridge Defend has a feature to control fan(s) that are placed behind the refrigerator to provide extra cooling to the coils behind the fridge and it seems like you'd want to use these controls for your vent fan.
(Side note: I'm also planning a DIY modification for putting fans behind the refrigerator controlled by a separate thermostat.)
SJ-Chris wrote:JBarca wrote:
Another reason for the Fridge Defend not yet mentioned is cold weather. I know you may not camp in cold down to freezing, and below, but in our area, freezing temps are here and we do winter camp.
If you want to get close to 32F outside or go below, the fridge as it stands in the stock configuration will slow down and may stop working. The heating may not stop, but the fluid can slow down flowing from what I have read. It seems Dometic does offer a lower vent hood that has some blocked off vents to lower the amount of cold air entering.
This Dometic lower vent is made for cold weather, just they do not list much else or fit the older Dometic vent frames. Norcold sells a cold weather kit to heat up a certain return tube on the cooling coil. Here is one of them. https://www.amazon.com/Norcold-634913-Cold-Weather-Kit/dp/B00T36VI30
I have not been able to find Dometic offering that heat strip. By using the heat strip on the Norcold and helping to reduce the cold air intake, it is reported you can go down to 0F. Some folks use an incandescent light bulb in the outside compartment.
The ARP system will help to shut off the boiler heat if the coolant stops flowing due to the cold weather for any reason.
Doug may be able to add some more to this and if he knows if Dometic offers a cold weather kit or do you just use the Norcold one? Most all of the older campers I restore have RM2652 fridges that I service.
Thanks
John
I will admit, I had not thought about ultra cold weather usage. I have been camping down to ~30*F and didn't have any issues with the refrigerator/freezer temps. I don't have immediate plans to camp down to 0*F. I'm guessing that the boiler getting hot to the touch does a fair job heating the cavity/space behind the refrigerator. But I can see how if it were 0*F outside and that cool air is being pulled in then maybe it could affect the cooling unit functionality. If I was going to camp in such temps I think I would consider putting something along the back side of the rear vent to limit the amount of air that could enter. That seems like it would allow the heat of the boiler to keep the air behind the refrigerator warm enough for proper operation. Not sure if that is true or not, but I'd start there.
I am big on safety. I do think it is important for safety and also to help protect your cooling unit from overheating damage to have some sort of high temp thermostat (either DIY or Fridge Defend) on your boiler to keep it below 220*C (428*F).
-Chris
โNov-18-2022 07:42 AM
Vintage465 wrote:
I guess today I'm going to "be that guy"........I grew in a family that owned an RV sales and repair shop.....in the days that if you ran your fridge out of level(propane or electric)it would lockup in 20 minutes. The law was "not level, don't light". The repair was to remove the fridge turn it on it's head for 24 hours, reinstall and fire it up...level of course. 99% of the time it fixed it. So my question is, why hypothetically set your self up to do damage to your fridge when it just needs to be level. Yes I get it that driveways and streets aren't level, but.........I'll stick by "not level, don't light".
โNov-18-2022 05:45 AM
โNov-17-2022 09:39 AM
otrfun wrote:SJ-Chris wrote:Have you found a suitable 200c sensor and control board combination that operates on 12vdc? IMO realworld temperature accuracy and overall, proven reliability may potentially be the biggest hurdle.
. . . I'm a DIYer and I enjoy tinkering with modifications . . . I believe a simple high temp thermostat can easily accomplish this task, and they only cost $20. If I only had 1 RV I would probably still just buy a Fridge Defend. But I've got 3 RVs. So if I can implement this DIY fix it will save me 3x the money.
Who wouldn't love a reliable, low-cost alternative to the $200+ FD?! ๐
โNov-17-2022 08:47 AM
SJ-Chris wrote:Have you found a suitable 200c sensor and control board combination that operates on 12vdc? IMO realworld temperature accuracy and overall, proven reliability may potentially be the biggest hurdle.
. . . I'm a DIYer and I enjoy tinkering with modifications . . . I believe a simple high temp thermostat can easily accomplish this task, and they only cost $20. If I only had 1 RV I would probably still just buy a Fridge Defend. But I've got 3 RVs. So if I can implement this DIY fix it will save me 3x the money.
โNov-17-2022 06:04 AM
โNov-16-2022 09:15 PM
JBarca wrote:
Chris, I have been following your post.
I did review the ARP system a while back, just never made it to installing any, yet. I called and talked with them today. They are very down to earth, and they are a, know what they are doing company.
JBarca wrote:
I am going with the Fridge Defend V5.11 with the fan control. I want to add the defrost fans inside the fridge and to cycle them you need the fan control version. The V5.11 has an alarm, so you know when you have a problem and you and tweak the settings as needed. Since most all the fridges I work on are older, there may be some level of coolant damage from prior owners, so the fridge may have limited life, but having the fire safety part is a big plus.
JBarca wrote:
Since I already have a fan up on the roof vent and a thermal disk switch to turn it on and off, I may switch the roof vent fan to the Fridge Defend. You just parallel the inside defrost fans with the roof vent fans. The ARP fan relay is rated at 20 amps, plenty for the milli amp fans I use, and the ARP defrost fans.
JBarca wrote:
Another reason for the Fridge Defend not yet mentioned is cold weather. I know you may not camp in cold down to freezing, and below, but in our area, freezing temps are here and we do winter camp.
If you want to get close to 32F outside or go below, the fridge as it stands in the stock configuration will slow down and may stop working. The heating may not stop, but the fluid can slow down flowing from what I have read. It seems Dometic does offer a lower vent hood that has some blocked off vents to lower the amount of cold air entering.
This Dometic lower vent is made for cold weather, just they do not list much else or fit the older Dometic vent frames. Norcold sells a cold weather kit to heat up a certain return tube on the cooling coil. Here is one of them. https://www.amazon.com/Norcold-634913-Cold-Weather-Kit/dp/B00T36VI30
I have not been able to find Dometic offering that heat strip. By using the heat strip on the Norcold and helping to reduce the cold air intake, it is reported you can go down to 0F. Some folks use an incandescent light bulb in the outside compartment.
The ARP system will help to shut off the boiler heat if the coolant stops flowing due to the cold weather for any reason.
Doug may be able to add some more to this and if he knows if Dometic offers a cold weather kit or do you just use the Norcold one? Most all of the older campers I restore have RM2652 fridges that I service.
Thanks
John