smkettner wrote:X2
DC fuse board s/b fine with existing. If pulling wire go with #6 wire. Maybe #4 if you want to kill it.
I would go #4 for that converter/inverter combo. Same for interconnects.
โSep-11-2014 08:15 PM
โSep-11-2014 08:00 PM
โSep-11-2014 07:00 PM
sjturbo wrote:
I am putting together four series/parallel GC batteries and need some help with cable sizing. Batteries are all side by side, converter will be within 3'of batteries, inverter should be within 4', but the DC fuse board is 15' to 17' away. Am I correct that all "series" lengths need to be the same. And the same for the parallel lengths? And the lengths from the batteries to the converter and inverter?