Biggest converter for Honda 2000
landyacht318
I am trying to assist someone else.
They are getting a Honda 2000 watt generator.
What is the biggest converter that it will be able to handle when charging 3 pair of depleted GC 6v batteries, lets assume 1500 feet above sea level?
Thanks
23 REPLIES 23
landyacht318
Thanks for the input
The person is intending to boondock 29 days out of 30, and is unsure how much they are going to consume. I've informed him of the 50 to 80 or 50 to 90 philosophy, and the importance of the occasional true 100% recharge, though I am not sure he knows the converter is not going to be doing EQ cycles and that the 30th day requires grid power or running the genny long enough to max out the SG. if he hopes to achieve a good battery lifespan. I also pointed out that the cost of gas to take batteries back to 100% by generator will cost more than replacing the batteries more often but he says he will find some grid power once a month to plug in and do what he has to do to get the SG up as high as it will go
For the shortest generator runtimes to reach 80%+, I've recommended the powermax 100 amp as its 1440 watts figure is still below 1600 watt maximum of the honda 2000.
msiminoff
What is the biggest converter that it will be able to handle when charging 3 pair of depleted GC 6v batteries...
Theoretically the EU2000i should be able to power a 125A power factor corrected converter long enough to charge that ~600Ah battery bank or a 150A PFC converter for a few minutes. The issue is that most converters are not PFC.
I don't own a "converter", but my Honda has no problem charging my batteries at a true 100A via my (PFC=0.99) inverter/charger, even at 6000ft.
Cheers,
-Mark
'04 Alpenlite Saratoga 935, 328W of solar, 300Ah Odyssey batt's, Trimetric, Prosine 2.0
05 Ram3500, Cummins,Vision 19.5 w/M729F's, Dynatrac Hubs, RR airbags w/ping tanks, Superhitch, Roadmaster Swaybar, Rancho RS9000XL
The Overlhander Blog
pianotuna
Nomad III
Nomad III
Hi,
The power factor on the PD units is 0.7
1600 watts is only going to power a 1120 watt PD converter running flat out.
That suggests to me that the PD9260 is a "safe bet".
Regards, Don
RoyB
The front panel of the Honda EU20001 says 13.3AMPs at 120VAC... That is around 1600WATTS...
I use my 2KW Honda to re-charge my three 85AH batteries in parallel using a PD9260C COnverter. I read 52-53AMPS DC Current being drawn by my battery bank for about 10 minutes then it start dropping back.
I can recharge my three batteries back up to the 90% charge state with-in a three hour run time on my 2KW Generator.
I think the PD9280 Converter input watts is around 1300WATTS at 120VAC so the 2KW Honda Generator should run that ok. IT does however state you should plug the PD9280 converter into a 20AMP receptacle, I think the 2KW Honda Generator only has a 15AMP 120VAC receptacle on it....
I suspect you do not have enough WATTAGE capability from the 2KW Honda Generator to re-charge your battery banks back up to 90% charge state in a three hour generator run time period. The rule of thumb is somewhere around 20AMPs of DC current for each battery in your bank to obtain a 90% charge state in a short three hour generator run time.
Maybe the experts will dime in here on what you need to make it work...
Roy Ken
Roy - Carolyn
K9PHT (Since 1957) 146.52M
2005 Flagstaff 8528RESS
ScottG
60 amp converter is the max, an 80 draws too much power.
wa8yxm
3 pair of GC-2 batteries can suck about 180-200 amps of power if you can find a converter that big.. I do not think you will.
A 1,000 watt GENRAC portable generator (True 1,kw) can power a PDI 9180 with a single pair of dead GC-2's. I know. I killed them and restored them to charge.
I would say 150 amps is possible with a Honda 2000, (Not a true 2kw generator)
But I do not think you will find a converter that big.
BFL13
Fisherguy's PD9280 drops to 75a at start and settles between 75-70 for a time before tapering off. (like a typical PD) that might help with the generator. ISTR the gen has some sort of surge allowance above that 1600 continuous for a certain time, which might be enough time for the PD to taper. However I don't know if it wouldn't run a straight 80 anyway. The PD9280 needs a 20a circuit not a 15a circuit.
1. 1991 Oakland 28DB Class C
on Ford E350-460-7.5 Gas EFI
Photo in Profile
ktmrfs
BFL13 wrote:
I think Fisherguy runs his PD9280 (non-PF corrected) with his. Probably can run the PF corrected PowerMax 100amper or WFCO 68100.
For near max load with a cold gen I recommend leaving Eco off at first, then turn Eco on a few minutes later.
I know the PD60A runs fine and gives the honda some margin, that's what I have. When I looked, the powermax PF corrected 100A should also work fine, maybe even better than a PD60A. I considered the PD80A, and couldn't convince myself I'd be able to run it at a full 80A. Problem is/was that PD doesn't spec VA draw, only watts, so it's a guessing game. I guessed it would be near the honda 1600VA max. but couldn't determine if it would be "above" or "below", so I went the the 60A.
However if Fisherguy runs his, sounds like it's an option and you've got a definitive answer. However, anything more than 80A Non PF corrected probably is going to be a problem.
2011 Keystone Outback 295RE
BFL13
Photo in Profile