Boondocker BPC4-60 Breakers

vicmic1983
Explorer
Explorer
I am replacing my old Magnetek 7300 with the recommended replacement the Boondocker BPC4-60. I have sent to emails to Randy at Best Converter and no response! My 7300 had the following breakers, 1 30-15 Tandem and 2 15-20 Tandems. The Breaker diagram for the Boondocker appears to indicate that the main is a double 30 however there is no information to tell exactly what the main configuration is. Any help out there?

34' Skyline 5th wheel triple slide 50 AMP.
1999 Dodge RAM 2500 Diesel
5000# Air Bags
Edge with Attitude
Tekonsha Brake Control
53 AUX Fuel Tank
Tire Pressure Monitor
20000K Hitch
HD Torque Converter
Extendable Power Mirrors
2 REPLIES 2

time2roll
Nomad
Nomad
Double 30 is wrong regardless of the diagram. Assuming the breakers do not swap over just get same rating as the existing. #14 wire needs 15a, #12 wire needs 20 amp, main at 30 amp will be #10 wire.

http://www.bestconverter.com/Boondocker-4-Stage-Power-Center-BPC4-60

ScottG
Nomad
Nomad
Everything goes through the main and more than likely, the converter is connected to it.
Are you replacing the entire panel?
Usually we just swap the converter section and keep the panel with breakers and fuses.