2005 Mobile Suites fifth wheel 36 ft with typical Dometic set up. Zone 1 Living area has 15K A/C with HP. Zone 2 is Bedroom with 13.5K Air conditioner only. Both are OE, Furnace is 42K all hooked together with a 5 button CCC thermostat.
Zone 1 works perfect. Furnace works almost perfect.
Zone 2 will run for ever on Fan only low or high
Zone 2 will run forever on Air conditioner on Fan low or on Automatic if difference between set temp and room temp is small enough to keep fan on low.
On Fan high or Auto with wide spread in temp the fan will start, the compressor will kick in and the unit will cool and run normally FOR NINE MINUTES. Then the fan will lock and the compressor will hummm. I don't know how long it will hummm as I always turn stat to zone 2 off before it pops a breaker.
Both capacitors check OK on my tester. I replaced my fan motor after I found some black windings and some burnt paper in it. That did not help and is a job I probably won't do again. I have two stats. One is a spare and it does it with either. I've checked all wiring and connections but it seems that if it was a bad connection it wouldn't start and run for nine minutes. I'm running only the one air conditioner and nothing else on my 30 amp home RV pad, but the problem started last winter in Florida on a robust 50 amp site.
I suspect the control board. I replaced it a couple years ago when the same air conditioner was running on it's own and not stopping until I pulled the circuit breaker. The board fixed the problem but there is one more small clue that puzzles me. When I installed the new board HEAT PUMP came up as a setting on the zone 2 tstat. It has no HP and never has and according to my Dometic manual no setting will be on the tstat that is not available.
Could they have given me the wrong board? Pretty sure I would have examined them pretty closely but I am 75 so you never know.
I have ruled out a compressor problem because it stays on when the fan shuts down. I have searched on all the on line forums I can find including 28 pages of posts by Doug. I not only can't find a solution I can't find anyone reporting the same problem.
I am open for suggestions.
Just another "bitter clinger"