pianotuna wrote:
If you have LOTS of the 10/2 then run at least 3 sets of 10/2. That may end up giving you the same voltage drop as some where between #8 and #7. (yes I know #7 doesn't commonly exist).
I used double runs of 10/2 for the solar panels to lower voltage drop.
โMar-18-2018 09:15 AM
โMar-18-2018 08:49 AM
โMar-18-2018 04:03 AM
DrewE wrote:azrving wrote:
You cant run romex in PVC.
You most certainly can run Romex in PVC or other conduit per code, but it has some limitations with respect to things like fill factor. This may be done, for example, to provide physical protection to an exposed section of a wire run.
What you can't do is run Romex, or some other "dry locations only" wire, through a conduit and have it magically become suitable for wet or damp locations. Conduit through wet or damp locations, such as outside or underground, requires wires inside it that are suitably rated for that sort of environment. Sometimes people get confused by this and take it to mean it's never permissible to run Romex through conduit since that's one of the primary places where conduit is required in typical residential wiring.
As a practical matter, pulling solid (non-stranded) cable through conduit is often impractically difficult, particularly if there's much other than a pure straight line run. It's just not that flexible.
โMar-17-2018 11:00 PM
azrving wrote:
You cant run romex in PVC.
โMar-17-2018 07:03 PM
SaltiDawg wrote:wa8yxm wrote:
...
And by the way that is the answer, If they fit then YES
This is not correct by Code.
โMar-17-2018 05:14 PM
wa8yxm wrote:
...
And by the way that is the answer, If they fit then YES
โMar-17-2018 03:25 PM
โMar-17-2018 03:03 PM
Bud
USAF Retired
Pace Arrow
โMar-17-2018 02:42 PM
Lon-Str wrote:
Sorry I didn't make myself more clear. The reason for the 1 1/2 conduit is that I already have it. I am running 150' of 10/2 (already have it). Just wanted to know if it was ok to add another 10/2 roll in the same conduit. Thanks. Like I said, I'm a little out of my element here.
โMar-17-2018 02:16 PM
โMar-17-2018 01:31 PM
โMar-17-2018 01:27 PM
โMar-17-2018 01:23 PM