MEXICOWANDERER wrote:
Again I shall ask this a different way...
The autoformers can INCREASE voltage when needed
Can they also DECREASE voltage when needed?
โJun-28-2015 11:27 AM
โJun-28-2015 10:28 AM
DrewE wrote:
I suspect there are not two taps, but rather that 32V boost comes if you use it in a 240V circuit and 16V in a 120V circuit.
By the way, I suspect the barn is well over 40 years old. A subpanel in the mid 70's would not typically have screw-in fuses, and a large barn built at that time likely would have had more than a 30A 240V service installed. (At least in this part of the country, an old barn is more like 100 or 150 years old and built with post-and-beam construction.)
โJun-28-2015 10:17 AM
pianotuna wrote:
Hi,
Do you know if the QC50ESCB is wired in as an autotransformer?
โJun-28-2015 10:15 AM
enblethen wrote:
What type of wiring goes between the house and the barn? It could be possible and less expensive to have this wire upgraded especially if it is aerial. Underground cost would be too high.
Did the electrician say which of the two taps he used? 16 or 32? If he used the 32, he could switch to the 16 and see what the levels are.
โJun-28-2015 10:11 AM
โJun-28-2015 09:11 AM
Bud
USAF Retired
Pace Arrow
โJun-28-2015 09:04 AM
โJun-28-2015 08:46 AM
โJun-27-2015 03:48 PM
Old-Biscuit wrote:
Gdetrailer........
You left out part of OPs statement
"The electrician installed the 30 AMP plug and we plugged in the Lodge, but my Good Governor showed that only 104 AMPS were coming into the Lodge. We then had the electrician install a power booster...." (OP meant VOLTS)
SO barn was getting low voltage to begin with.
Electrician should have noted that it wasn't adequate for 15A let alone 50A/30A etc.
Wire size is TOO SMALL
โJun-27-2015 02:44 PM
โJun-27-2015 02:33 PM
โJun-27-2015 02:06 PM
Old-Biscuit wrote:smkettner wrote:
If all is good and still have the voltage drop the wire is probably inadequate even for 30 amp.
Wire is inadequate for 15A.........measuring only 104V prior to voltage booster installation.
Electrician did OP wrong.
โJun-27-2015 01:22 PM
smkettner wrote:
If all is good and still have the voltage drop the wire is probably inadequate even for 30 amp.