Trying to get a idea hove long a Honda EU 3000is will run on a tank of gas whith a 15000 btu air conditioner running using about 14A, so a bit more than 50% load, I have a Magnum hybrid MSH 3000 for start up loads. 520A of battery's and 600W of solar Honda writes 7.2 H at rated load and 20 H at 1/4 load. Thanks Frank.
Frank
2012 F250 XLT
4x4 Super Cab
8' Tray 6.2lt, 3.7 Diff.
5 REPLIES 5

JaxDad
Explorer III
Explorer III
Load is based on whether the A/C is cycling or just running the blower.

Typically the A/C won't be running non-stop unless you are in full sun on a hot day.

bgum
Explorer
Explorer
8-9 hours based on experience. It will be impacted by outside temp and inside temp and how much does the compressor on the AC run.

Sandia_Man
Explorer II
Explorer II
Being a sizable load for the Honda 3000is, I would expect the longevity of a filled tank to be closer to the hours stated at near max rated load than the 1/4 load rating. Hard to say for sure with the variables involved, maybe 10 hours give or take. Our Onan consumes about 1/2 gallon and hour while our Champion 3100 inverter genny will power our 13.5K AC unit nearly 7 hours on it's 1.5 gallon tank.

Old-Biscuit
Explorer III
Explorer III
Per Honda

*Fuel Tank Capacity 3.4 gal.
*Run Time per Tankful 7.1 hrs. @ rated load, 20 hrs. @ 1/4 load
*Rated Load 2.8kVA (2800W/23A)
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

donn0128
Explorer II
Explorer II
What does the owners manual say?