Jim McGarvie wrote:In addition to the other suggestions, if you are using a Progressive Industries EMS, you might have an unbonded neutral on your generator and the EMS will not allow power into the coach in that situation.
Thanks for the reply. No, it is an Intellitec EMS. Interestingly, turns out the original problem with the pedestal (and two others) was an unbounded neutral. That has been fixed but we can't use the pedestal or the generator due to the damage incurred, probably to the EMS.
Jim
โAug-03-2019 12:12 PM
Bud
USAF Retired
Pace Arrow
โAug-03-2019 11:54 AM
In addition to the other suggestions, if you are using a Progressive Industries EMS, you might have an unbonded neutral on your generator and the EMS will not allow power into the coach in that situation.
โAug-03-2019 11:49 AM
enblethen wrote:
Are you disconnected from the shore power?
Remove shore power from pedestal. The transfer switch could be seeing power to hold it in shore powr and not allowing to go to genset.
Pedestal back to the sservice point is responsibility of the park. If it was the power utility problem, you would not be the only one effected.
Sounds like an open neutral in park system.
โAug-03-2019 11:46 AM
BFL13 wrote:
Are you using an inverter/charger and if so what model? The 120v pass-through of the inverter part might need some sort of reset.
โAug-03-2019 07:35 AM
enblethen wrote:
The transfer switch could be seeing power to hold it in shore powr and not allowing to go to genset.
โAug-02-2019 08:29 PM
Jim McGarvie wrote:
Any ideas?
โAug-02-2019 07:13 PM
Bud
USAF Retired
Pace Arrow
โAug-02-2019 07:07 PM