Salvo wrote:
The probability of 2 faults occurring is much greater than just one fault. That why the unbonded system is a lot safer. You don't need to rely on the GFI to work. They do fail.
BTW, the unbonded system has the same protections in regards to circuit breaker and GFCI. Add GFCI then three faults need to occur to get an "ouch". That system is virtually bullet proof. I'll take my chances any day of the year with those odds.
Should ground short to neutral or to hot (which isn't any big deal), I believe the 3-lite ac tester will pick it up.
SalSCClockDr wrote:
With the generator neutral & ground un-bonded:
If the neutral happens to short to ground and you make contact with the hot while grounded, ouch!
If the hot happens to short to ground and you make contact with the neutral while grounded, ouch!
If bonded then a hot to ground short trips the breaker on overload & a neutral short to ground will trip a GFCI breaker or outlet on ground fault if it is between the short and the bonded source.
โJul-02-2013 08:04 PM
Wayne Dohnal wrote:AFAIK I'm the only one on the forum who has taken the position that there's not a clear "winner" with bonded vs. unbonded. With some faults, unbonded is clearly safer. With other faults, as noted above, unbonded just masks the problem and creates a hazard at the same time. If you don't know what fault your system is going to have, you don't know which is the better way to go. Fortunately, faults are rare, which I why I believe that either method is permitted with small generators. If one way or the other were clearly superior I assume the codes would be changed to require it.
If the hot happens to short to ground and you make contact with the neutral while grounded, ouch!
If bonded then a hot to ground short trips the breaker on overload & a neutral short to ground will trip a GFCI breaker or outlet on ground fault if it is between the short and the bonded source.
โJun-30-2013 12:07 PM
SCClockDr wrote:
With the generator neutral & ground un-bonded:
If the neutral happens to short to ground and you make contact with the hot while grounded, ouch!
If the hot happens to short to ground and you make contact with the neutral while grounded, ouch!
If bonded then a hot to ground short trips the breaker on overload & a neutral short to ground will trip a GFCI breaker or outlet on ground fault if it is between the short and the bonded source.
โJun-30-2013 07:43 AM
smkettner wrote:Jbird wrote:
Thanks folks. After reading the link re grounding generators I see I have had the open ground issue with a generator for 9 years thru two fivers and have just now discovered it because of other electrical problems. So it's either not to worry or Im living on borrowed time when using my generator. The link seems to encourage either view. Thanks again
What are the other issues? We can help with those but the rest is normal.
โJun-29-2013 09:56 PM
AFAIK I'm the only one on the forum who has taken the position that there's not a clear "winner" with bonded vs. unbonded. With some faults, unbonded is clearly safer. With other faults, as noted above, unbonded just masks the problem and creates a hazard at the same time. If you don't know what fault your system is going to have, you don't know which is the better way to go. Fortunately, faults are rare, which I why I believe that either method is permitted with small generators. If one way or the other were clearly superior I assume the codes would be changed to require it.
If the hot happens to short to ground and you make contact with the neutral while grounded, ouch!
If bonded then a hot to ground short trips the breaker on overload & a neutral short to ground will trip a GFCI breaker or outlet on ground fault if it is between the short and the bonded source.
โJun-29-2013 08:25 PM
โJun-29-2013 04:58 PM
โJun-29-2013 04:02 PM
Jbird wrote:
Thanks folks. After reading the link re grounding generators I see I have had the open ground issue with a generator for 9 years thru two fivers and have just now discovered it because of other electrical problems. So it's either not to worry or Im living on borrowed time when using my generator. The link seems to encourage either view. Thanks again
โJun-29-2013 04:00 PM
Jbird wrote:
When testing my coach outlets with a plug in tester it indicates " open ground" on all circuits when I am powering with my portable generator. The GFI circuits do not break but show the same open ground. My tester plugged directly into the Honda generator also shows open ground.
A different power source to my coach, all circuits test properly. Can anyone explain why I show open ground in coach and at generator and am I in any danger in coach using generator for power. Thanks to the knowledgeable in advance
โJun-29-2013 02:47 PM
โJun-29-2013 11:48 AM
rockhillmanor wrote:
'Why' does a generator need to be and/or is not grounded?
โJun-29-2013 11:36 AM
'Why' does a generator need to be and/or is not grounded? I ask not being an electrician so go easy on me.Here are some threads about it from before the time I was burned out over it. Some of the posts fit "go easy", others don't. As you can see, it's not a new issue.
โJun-29-2013 10:35 AM
We must be willing to get rid of the life we've planned,
so as to have the life that is waiting for us.
โJun-29-2013 09:17 AM
Jbird wrote:
So it's either not to worry or Im living on borrowed time when using my generator.