Bud
USAF Retired
Pace Arrow
โOct-11-2018 01:06 PM
185EZ wrote:
sunavabitch
That was it
I had to rotate the 30 amp outlet to make the wires reach but it also makes it easier to plug in the cord. The way they had it was difficult to plug in. I almost bought an adapter.
No more codes on EMS and it sent power through.
Would there be any damage to my rv when I had it plugged in directly to the generator with those wires switched?
Everything seemed to work fine
Tied inside makes sense, but what I meant was that the 20A receptacles selected one of the output legs as neutral and the 30A receptacle selected the opposite one.
โOct-11-2018 11:54 AM
โOct-11-2018 11:18 AM
Bud
USAF Retired
Pace Arrow
โOct-11-2018 11:00 AM
โOct-11-2018 10:41 AM
โOct-11-2018 10:27 AM
โOct-08-2018 08:26 PM
pnichols wrote:Anything is possible until it's tested. I'll just say I've had 2 dometic fridges that didn't care about the bond, and I've never noticed a report of any RV fridge caring about it.
Could this be that the Norcold refrigerator's control board is sensitive to the little generator's output not having it's neutral bonded to it's ground ... as is being dicussed here?
โOct-08-2018 06:17 PM
wnjj wrote:185EZ wrote:
There's continuity between all of them.
upper left on the 20A and lower right and left on 30A
same with upper right pins on 20A and continuity between lower right and left on 30A
also continuity between all grounds
Yes it's a misprint of 240V in the specs.
There isn't even a switch for it.
The old Durostar had the 240V switch and that was one of the reasons I wanted the EMS in case the switch was accidently turned on
This makes even less sense. Of course when I say "continuity" I'm assuming an ohm meter that's reading near 0 ohms, not a handful or more through a coil. I should have been more clear.
Also, without your bonding plug in there, the grounds should connect to nothing but each other and the ground lug.
โOct-08-2018 06:02 PM
185EZ wrote:
There's continuity between all of them.
upper left on the 20A and lower right and left on 30A
same with upper right pins on 20A and continuity between lower right and left on 30A
also continuity between all grounds
Yes it's a misprint of 240V in the specs.
There isn't even a switch for it.
The old Durostar had the 240V switch and that was one of the reasons I wanted the EMS in case the switch was accidently turned on