kellertx5er wrote:That relates to a Solar Grid Tie inverter that shuts down when utility power is not present.
" its against code and dangerous to back feed the main panel from the inverter"
NEC Article 690 specifically ALLOWS an inverter to backfeed into the service panel (690.10(C)).
" use dedicated NEW circuits for inverter output"
That's exactly what the OP is proposing to do.
If equipment is properly labeled to indicate multiple power sources, this arrangement is acceptable.
โNov-04-2016 02:54 PM
โNov-03-2016 08:20 AM
โNov-02-2016 06:35 PM
โNov-02-2016 05:06 PM
โNov-02-2016 02:37 PM
โNov-02-2016 02:24 PM
โNov-02-2016 01:56 PM
MrWizard wrote:
need some more info, what are you trying to do ?
its against code and dangerous to back feed the main panel from the inverter
use dedicated NEW circuits for inverter output
Or
use a sub panel for the inverter output, move circuits to the sub panel
Or
use a transfer switch between inverter and existing breaker output to feed existing circuit