rjniles wrote:
Article 551 has been discussed in a few of theses posts.
A minimum of two RV spaces are required to use Article 551 for site wiring.
The feeder to the RV panel is required to be sized for the expected loads. That doesn't necessarily mean a full 50 amps, but it doesn't necessarily mean 30 amps is sufficient either. What is the actual load of the RV and what is the actual load of the equipment you wish to connect to the 20 amp receptacle?
By installing the new RV panel you are changing this circuit from a branch circuit to a feeder. That means you will need to install two ground rods at the new panel. That's the impact not using Article 551 has on you. 551 does not require ground rods, but not using 551 requires them to be added.
โAug-20-2017 10:47 AM
โAug-20-2017 08:41 AM
โAug-20-2017 08:14 AM
โAug-20-2017 08:08 AM
Bud
USAF Retired
Pace Arrow
โAug-20-2017 07:25 AM
enblethen wrote:
If you look at 551, you will find that you must also follow parts I, II, III, IV and V of the code.
โAug-19-2017 11:50 AM
โAug-18-2017 06:20 PM
โAug-18-2017 05:44 PM
Bud
USAF Retired
Pace Arrow
โAug-18-2017 04:42 PM
enblethen wrote:
Soren:
You may want to look at Art 225 II 225.30
โAug-18-2017 04:36 PM
myredracer wrote:soren wrote:I will tell you one thing for certain, I would never ridicule anyone on a forum simply because I did not agree with their opinion, esp. if I thought my opinion is superior because I happened to think I have more training, education, experience or qualifications. And I would never post any comments along with a note that I am a PE (ever...).
Electrical questions are always pretty entertaining on the forum, usually because there are plenty of wrong answers, but this one is in a league of it's own.
You want to guess how many times members here have, in the past, recommended doing things like hooking up a 30 Amp. trailer receptacle to a 240V feed? I'll give you a clue, it's far from unusual. I would have no issue with calling out a member who recommended a pressurized water line repair with duct tape, if I was a plumber, or a recommendation to put bacon grease on a second degree burn, if I was a nurse. Because you have access to a keyboard, and an opinion, it doesn't mean your opinion is safe, correct, or remotely in keeping with standard, let alone best practice. As for your claim of never mentioning your qualifications and experience, do I need to paste the fact that you did just that, a few posts ago?soren wrote:The OP's initial query is of a pretty basic & simple code nature. How are comments like the above and others you've made helpful in clarifying the OP's situation. I even commented that the OP could go to the Mike Holt electrical forum (where there are electricians, engineers, inspectors and other electrical experts) if he still had any doubts. How many homeowners even take out a permit to install an RV recept./pedestal? Not interested in debating the different methods for wire pulling and when to.
How many of you would expect to find pairs of massive feeder conductors, as in 3/4" diameter wires, bolted inside of a 50 Amp pedestal, with no breaker that size anywhere. How many understand a ten foot tap rule? RV park wiring has lots of things a typical residential electrician might find odd, or even wrong.
As I noted earlier, ALL of this depends on the local inspector, and they may be extremely competent, or clueless.
eom...