tobydog927 wrote:herbhyde wrote:tobydog927 wrote:
It could still be the breaker, sure, but it's been 24 hours now without a single power trip, since the water heater has been off.
I finished all the foil & foam thing over my outside water hose yesterday, woke up expecting water. Nothing. Giant icicles down the foam covered hose leading out from the trailer, lots of ice. Not sure why it's leaking there in the first place to make that much ice, but any suggestions?
Broken water lines due to freezing. You just made your problem a lot worse. You sound as if you are on a limited budget. Right now the trailer is not livable.
What water lines? Everything works when the hose is thawed out
โDec-30-2015 08:09 AM
herbhyde wrote:tobydog927 wrote:
It could still be the breaker, sure, but it's been 24 hours now without a single power trip, since the water heater has been off.
I finished all the foil & foam thing over my outside water hose yesterday, woke up expecting water. Nothing. Giant icicles down the foam covered hose leading out from the trailer, lots of ice. Not sure why it's leaking there in the first place to make that much ice, but any suggestions?
Broken water lines due to freezing. You just made your problem a lot worse. You sound as if you are on a limited budget. Right now the trailer is not livable.
โDec-30-2015 08:07 AM
tobydog927 wrote:
It could still be the breaker, sure, but it's been 24 hours now without a single power trip, since the water heater has been off.
I finished all the foil & foam thing over my outside water hose yesterday, woke up expecting water. Nothing. Giant icicles down the foam covered hose leading out from the trailer, lots of ice. Not sure why it's leaking there in the first place to make that much ice, but any suggestions?
โDec-30-2015 07:54 AM
โDec-29-2015 02:43 PM
โDec-29-2015 09:48 AM
โDec-29-2015 08:42 AM
herbhyde wrote:tobydog927 wrote:Boband4 wrote:
The OP has continously remarked that everything is electric, no gas-and it has been cold and windy. Could the electric side of the water heater be cycling on more? The water heater in conjunction with the space heater and electric blanket would probably overload a 30 amp circuit. Recommend the OP look for the water heater and see if there is an on/off switch.
I do hear the water heater often outside once I've had to reset the breakers after it trips. Even if I haven't used any hot water in hours or all day. I have noticed my hot water somewhat sprays/spits out of the tap in the kitchen at first occasionally, it never used to do that.
Do your suggest if there is an on/off switch to only switch it on as needed, like to shower? Not sure how long prior to a shower it would need to heat though, I will take a look for the switch today, if there is one.
Where does the water pressure come from??? An external hose(Well Pump)
or the water pump in the TT.
โDec-29-2015 08:20 AM
tobydog927 wrote:Boband4 wrote:
The OP has continously remarked that everything is electric, no gas-and it has been cold and windy. Could the electric side of the water heater be cycling on more? The water heater in conjunction with the space heater and electric blanket would probably overload a 30 amp circuit. Recommend the OP look for the water heater and see if there is an on/off switch.
I do hear the water heater often outside once I've had to reset the breakers after it trips. Even if I haven't used any hot water in hours or all day. I have noticed my hot water somewhat sprays/spits out of the tap in the kitchen at first occasionally, it never used to do that.
Do your suggest if there is an on/off switch to only switch it on as needed, like to shower? Not sure how long prior to a shower it would need to heat though, I will take a look for the switch today, if there is one.
โDec-29-2015 06:51 AM
Boband4 wrote:
The OP has continously remarked that everything is electric, no gas-and it has been cold and windy. Could the electric side of the water heater be cycling on more? The water heater in conjunction with the space heater and electric blanket would probably overload a 30 amp circuit. Recommend the OP look for the water heater and see if there is an on/off switch.
โDec-29-2015 06:48 AM
hohenwald48 wrote:
There are some things a good electrician could do to get you more than 30 amp service. However, some of them are "non-standard" installations and would depend on who has jurisdiction over electrical installations in your area and how flexible they are.
Although your extension cord is only 50' you are still using another 50' (or is it 100'?) of permanently installed "extension cord" which may or may not be up to the task. Voltage drop will also be impacted by the size of that wire. It's been my experience that a lot of ranches and farms have old wiring installed by folks who might not be fully qualified.
It sounds like your best bet, at the moment, is to lessen the load as much as possible, maybe run a second cord from another circuit to carry the heater load and check for "phantom" loads. ie: those you might not be aware of like battery charger, water heater, refer, heat tapes and other devices that draw on your available current.
It's possible you have a bad breaker but that is a very rare event regardless of what you read on internet forums.
Your next challenge will be finding a good, qualified electrician who is able to be "creative" in finding a safe and economical solution to your problem in the long run.
One more thing. The closer your trailer is to the breaker box (not just the outlet) the better off you will be and the cheaper a permanent solution will be. You might want to think about a move.
โDec-29-2015 06:44 AM
โDec-29-2015 06:16 AM
โDec-28-2015 08:44 PM
hohenwald48 wrote:
A 100' 14 gauge copper extension cord carrying a 20amp load will result in a little over 5 VAC drop.
You would do well to get some voltage readings with the heater in operation but it really sounds like you are just overloading the circuit. When you do that the breaker will trip.
Also, some of the info that has been given on here is correct and some is not. 50 amp service is two legs of 50 amp service providing a total of 100 amps for load. It is not 2 legs of 25 amps as someone stated. Find a good electrician and show him the link smkettner posted about RV feed wiring.
Actually, as long as there are no 240 volt loads in the trailer (and there probably is not) the two legs do not even have to be of different phases. However, the neutral size will have to be adjusted.