โJan-25-2015 05:12 PM
โJan-26-2015 07:06 AM
โJan-26-2015 07:01 AM
โJan-26-2015 06:43 AM
smkettner wrote:
Are you sure the electric side of the water heater was off?
Any chance you checked the voltage? Still odd for the 30 amp pedestal to trip before the 20 amp branch circuit if was as you said.
For best performance get the roof shroud off and see if the coils need cleaning.
โJan-26-2015 05:15 AM
โJan-26-2015 05:11 AM
โJan-26-2015 05:03 AM
โJan-26-2015 04:28 AM
โJan-25-2015 06:34 PM
ScottG wrote:
When everyone is using a lot of power in the CG, the parks voltage drops and that can cause the current to rise and trip the breaker.
So it's now your RV's problem, it's the parks - especially if it's an older under wired park.
You should monitor the incoming voltage and shut you AC off if it's too low as this will kill your AC and some other appliances.
We must be willing to get rid of the life we've planned,
so as to have the life that is waiting for us.
โJan-25-2015 05:19 PM
โJan-25-2015 05:15 PM