Ok, if the over limit switch trips or the furnace fails to light it is SUPPOSED to shut down so long as you have the OEM board. not sure that Dino Boards do that.
Now I knwo Atwood best. on Atwood if you open the outside access there is a switch (Actually a circuit breaker) on top of the blower housing. Turn it OFF, then set the Thermostat high enough so it will call for HEAT when it can.
Turn the switch on and observe the operation
Normal operation
Fan/Blower starts
Then you may hear the CLICK of the gas solenid and the Snap, Snap of the ignightor
Then it should FLAME ON and continue to produce heat.
Optional it may flame off, then re-start 2 more times then if you look at the control board you will see a flashing LED (post pattern).
IF you see that flashing led.. Post pattern.. IE 3 3 3 3 3