valhalla360 wrote:Old-Biscuit wrote:
100' with 50A #6 power cord 40A load will have roughly a 3-4 Volt drop from source to RV
120VAC....116/117VAC
You are assuming the house has good strong voltage and it won't sag under heavy load (and you are thinking 120v when a 50amp is 240v)
If the outlet is 50am, it should be 240V but don't be surprised to see 220v at the outlet.
At 220v, 20amp per leg jumps to around 22amps per leg (assuming the air/con units are on separate legs). So each leg sees 22amp @ 110v at the outlet and with voltage drop around 108v at the RV.
That's marginal for me where I start considering if should deploy the voltage booster or break out the generator.
If for some reason both air/con units are on the same leg, the amps doubles on that leg and voltage drop results in around 106v.
This ignores bad connections or issues with the wiring in the house, so you could easily lose another 2-3 volts in real life.
โOct-01-2020 08:22 AM
BB_TX wrote:supercub wrote:
.......
I'm trying to plug into a house with 50 amp plug. Thanks
I hope this is a 50 amp plug wired for an RV and not a 50 amp dryer plug.
โOct-01-2020 07:44 AM
โOct-01-2020 07:29 AM
supercub wrote:
.......
I'm trying to plug into a house with 50 amp plug. Thanks
โOct-01-2020 05:09 AM
โOct-01-2020 04:15 AM
Old-Biscuit wrote:
100' with 50A #6 power cord 40A load will have roughly a 3-4 Volt drop from source to RV
120VAC....116/117VAC
โOct-01-2020 02:16 AM
โSep-30-2020 10:44 PM
โSep-30-2020 10:42 PM
โSep-30-2020 10:15 PM
supercub wrote:Have someone measure the distance. Every 25 feet makes a big difference.
I'm trying to plug into a house with 50 amp plug. Thanks