BillofPA wrote:
One time I turned off the breaker to my washer/dryer combo and I had the same problem as the poster; only 30 amps available when plugged into 50. See signature: 2004 HR Ambassador
โSep-12-2016 08:41 AM
โSep-12-2016 07:49 AM
usersmanual wrote:The Progressive unit will not give alert that L1 & L2 are bonded.
I too thought the progressive unit would alert you if you were not receiving a real 50 amp connection?
โSep-12-2016 07:00 AM
โSep-11-2016 08:47 AM
Ed_Gee wrote:jswat wrote:
I am connected through a portable Progressive surge protector which shows correct wiring and 50 amps. Everything works inside the MH but I cannot run both a/c units unless I turn off something (like the water heater). The transfer switch has no problem switching between genset and shore power. Something is just not letting 50 amps through.
The question remains..... do you have 240VAC across the two 50A hot leads on the pedestal??? It is a simple measurement with your VOM....please report. It is unknown, to me at least, if the Progressive protector would give an error condition to same phase voltage across those two points so it's showing of "correct" 50A service is inconclusive.
โSep-11-2016 08:34 AM
jswat wrote:
I am connected through a portable Progressive surge protector which shows correct wiring and 50 amps. Everything works inside the MH but I cannot run both a/c units unless I turn off something (like the water heater). The transfer switch has no problem switching between genset and shore power. Something is just not letting 50 amps through.
โSep-10-2016 02:55 PM
โSep-10-2016 01:47 PM
โSep-10-2016 01:44 PM
โSep-10-2016 01:42 PM
โSep-10-2016 12:59 PM
โSep-10-2016 12:48 PM
rgatijnet1 wrote:dougrainer wrote:rgatijnet1 wrote:dougrainer wrote:
1. Doubt the Transfer switch is bad. It is extremely rare for a transfer switch to only close 1 leg of power.
2. Your EMS senses the OUT OF PHASE 2 -120 legs of power. IF those 2 legs are on the same phase, the EMS assumes you have 30 amp service
3. VERIFY that you have double the line voltage between the 2- 120 legs at the 50 amp service pole(3 and 9 position). IF NOT, you do not have 50 amp service. But, "Cheated" 50 amp service. Cheated is a 50 amp breaker on the same phase supplying ONLY power on a 50 amp breaker and not a TOTAL of 100 amps which is true 50 amp service
4. EMS systems do not have to be "set" to 50 amp service. It is Automatic when connected to true 50 amp service. You cannot even change to 30 or 20 if on 50 amp service.
Do these tests and post. Doug
My Intellitec EMS sytem has a button on the left side to allow me to select 30 or 20 amp service, even if I am plugged in to 50 amp service.
From the EMS manual. Doug
NOTE When connected to 50Amp-240VAC service the Energy Management features of the unit are disabled and the Unit switches all controlled loads"ON".
Besides, if ON 50 amp serviced(100 amps) WHY WOULD YOU WANT OR BE ABLE TO SET 30 0R 20 AMPS????????????????
Good point BUT why did the manufacturer put the button there to switch input. Before I posted I went to my panel and I can push the button and change to a lesser input power than what I am connected to. Apparently the manufacturer had some reason to do this. If it is all automatic, no push button would ever be needed.
โSep-10-2016 12:41 PM
usersmanual wrote:smkettner wrote:usersmanual wrote:
do you people even read the posts?? He clarified the problem
How could it be the EMS if it works perfectly on generator power
He says he can run 2 AC on generator but not on shore power
he says all service/outlets work both ways
his complaint as stated is he has to shut off(example) the HWH
when on shore power to run two AC units but everything works 100% on generator
EMS is registering 30 amp service. Typically a 30 amp adapter will connect both hots of the RV to the single hot of the 30 amp supply. This has zero volts between L1 & L2 in the RV. The EMS is cutting out various loads (normal load shed) because it thinks only 30 amp supply is available. Power would still be available to all items until the total exceeds the 30 amps when the EMS starts limiting.
Turn on the generator and the EMS knows it has full generator power.
So the first issue to verify is if the L1 & L2 of the pedestal has 240 (or 208) volts. Some are not wired properly. The specifics of the supply testing were not given.
yes I know and that's why I as you have asked the OP to meter across the 120V outs and make sure hes got 240V BUT what If he does have 240V then whats your opinions as to what is complaint is caused by?
My understanding and may be wrong is the EMS works on generater or SP
does it not?