marspec wrote:Bobbo wrote:marspec wrote:
When the generators were paralleled the EMS allowed hook-up and ran the AC. There was, however, an open ground message. HMMM!
This is puzzling. If there was an open ground, the EMS should not have allowed the hook-up. If there was no open ground, there should have been no open ground message.
Are you sure the open ground message wasn't a message from an earlier error? The EMS does keep displaying the error message from earlier even after the problem is corrected.
I would agree re prior error message except when a single gen was hooked up the error didn't appear. When paralleled the EMS displayed Line 1 voltage, Line 1 amps, Line 2 voltage, Line 2 amps, 60 cycles, E0, and then whatever the msg for open ground is EF2??
โJun-10-2014 02:31 PM
Bobbo wrote:marspec wrote:
When the generators were paralleled the EMS allowed hook-up and ran the AC. There was, however, an open ground message. HMMM!
This is puzzling. If there was an open ground, the EMS should not have allowed the hook-up. If there was no open ground, there should have been no open ground message.
Are you sure the open ground message wasn't a message from an earlier error? The EMS does keep displaying the error message from earlier even after the problem is corrected.
โJun-10-2014 07:29 AM
marspec wrote:
When the generators were paralleled the EMS allowed hook-up and ran the AC. There was, however, an open ground message. HMMM!
โJun-09-2014 06:48 PM
โJun-09-2014 08:12 AM
โJun-09-2014 08:00 AM
โJun-09-2014 07:22 AM
marspec wrote:smkettner wrote:
For additional safety you can make the bond plug with a 100,000 ohm 1/2 watt resistor.
OK I wired a plug with the resistor and hooked a single generator to the fiver and got the no ground message. I doubt that using only a single gen should make a difference. I had a 98K reading between the ground and neutral plug. I've wired another plug without the resistor and will give that a try tomorrow. The generator was putting out 129V at 60 cycles. What voltage reading are others getting?
โJun-09-2014 05:45 AM
โJun-08-2014 07:50 PM
โJun-08-2014 07:42 PM
smkettner wrote:
For additional safety you can make the bond plug with a 100,000 ohm 1/2 watt resistor.
โJun-06-2014 02:59 PM
wa8yxm wrote:
Or use the bypass.. Question.. Will the bypass reset when power is removed (I believe it will)
โJun-06-2014 02:55 PM