Boomerweps wrote:Without the inverter on the shunt the battery monitor would not be very accurate.
I would not route inverter power via the shunt or buss bars (extra connections between the battery and inverter). Make it as direct & short as possible, just protection.
โOct-18-2023 06:39 PM
timelinex wrote:Boomerweps wrote:
Read the reviews on Amazon. Most complain about the wires supplied with inverters is TOO small, mostly 4 AWG.
Use at least 1/0awg or better yet, 2/0awg. If making your own, ask for the given gauge welding cables at your electrical supply store. Welding cable is very flexible with many smaller wires.
Another consideration is that many, myself included, decide that a given inverter is a little small and get a higher power unit. If the wiring is extra thick for the smaller inverter, it can support the larger unit.
IMO, the inverter should be directly connected to the battery bank with only a fuse or circuit breaker on the positive cable.
I plan on adding a BUS bar. Should I connect the negative end directly to my shunt and positive to my batteries...Or should I go through the Bus Bars, which add distance.
โOct-18-2023 03:46 PM
Bud
USAF Retired
Pace Arrow
โOct-18-2023 02:57 PM
โOct-18-2023 12:29 PM
โOct-18-2023 11:16 AM
Boomerweps wrote:
Read the reviews on Amazon. Most complain about the wires supplied with inverters is TOO small, mostly 4 AWG.
Use at least 1/0awg or better yet, 2/0awg. If making your own, ask for the given gauge welding cables at your electrical supply store. Welding cable is very flexible with many smaller wires.
Another consideration is that many, myself included, decide that a given inverter is a little small and get a higher power unit. If the wiring is extra thick for the smaller inverter, it can support the larger unit.
IMO, the inverter should be directly connected to the battery bank with only a fuse or circuit breaker on the positive cable.
โOct-18-2023 10:29 AM
โOct-18-2023 10:06 AM
โOct-18-2023 08:58 AM
โOct-18-2023 08:17 AM
โOct-18-2023 07:13 AM
timelinex wrote:
I have a 2kw inverter and will be getting a 100a converter for my 2 100ah lifepo4 batteries. Currently I'm just using whatever ga wires came with everything (a bix of 4/6/8).
I am planning on changing everything to connect through a BUS BAR and upgrade all the cabling to heavier ga. I want to future proof it to handle a 3kw inverter.
It's been REALLY confusing figuring out what wires I need. ALMOST everything online "(forums and articles) tell me I need something like a 4/0 guage, which is HUGE. That makes sense considering 3kw can reach 200-250 amps. Except the fact that no OEM items come with something nearly this thick.
I think the reason all these recommendations may be wrong is they do not account for length of wire being very short in our use cases.
It looks like considering everything is definitely under 4ft, I won't need anything over 4ga. On the other hand, I'm pretty sure that ampacity is over max 4ga rating when you look it up.
Can anyone make any recommendations based on actual knowledge and not just heresay or making best guesses?