Helping a friend of mine set up a new car hauler.Should a Honda EU3000IS generator have any problem running a new Coleman Mach 15 15000 btu roof ac unit?
2016 wildwood bunkhouse,2018 f150 5.0.Camping with the grandkids now.
I have a 8,ooo btu and was using my friends eu3000 and several times I thought it was going to stall it out in the middle of the night. The generator was just on the other side of my wall and I remember it making the hesitation/about to stall noise many times. Having said that, it did run my ac and lights most of the time without tripping its breakers. If your going to make a purchase of an eu3000 I would borrow one and try it first. When I was making a purchase the dealer offered to let me bring my rv and try it out first.
Papa Bob 1* 2008 Brookside by Sunnybrook 32' 1* 2002 F250 Super Duty 7.3L PSD Husky 16K hitch, Tekonsha P3, Firestone Ride Rite Air Springs, Trailair Equa-Flex, Champion C46540 "A bad day camping is better than a good day at work!"
If that's all that is running, should not be a problem. Good for 23.3 amps peak load, maybe a bit more. You may want to be sure no other loads are Ono it, and that Eco throttle is off. Main issue is starting the compressor. Any other loads planned?