โSep-06-2020 11:53 AM
โSep-07-2020 12:07 PM
Bud
USAF Retired
Pace Arrow
โSep-07-2020 10:21 AM
coolmom42 wrote:pianotuna wrote:
coolmom,
Driers may be 240 volts. Be extremely careful.
Yep.
Probably not the best idea. If I did it I would double check behind the electrician. Not a trusting person here!
I'll probably just get a separate circuit run, since the breaker box is a few feet from the dryer, and plenty of room in the breaker box. But will also double-check behind the electrician. ๐
Thanks for the warning.
โSep-07-2020 09:47 AM
Bud
USAF Retired
Pace Arrow
โSep-07-2020 09:22 AM
Bobbo wrote:way2roll wrote:
Why do you say the house current isn't enough? I run a 50/30/15 adapter and plug it into an exterior house outlet. As long as I am careful to run one AC only, no problem. Seems like this is more complicated than it needs to be unless I am missing something.
House loads on that circuit. He not only has to count RV loads, he has to count house loads too.
โSep-07-2020 09:12 AM
time2roll wrote:dougrainer wrote:The 14-30 connector has an L shaped neutral, 50a has a flat blade.
I would get a replacement RV MALE 50 amp end and install the standard 30 amp shore cord extension.
โSep-07-2020 07:46 AM
Bobbo wrote:Dryer circuit is virtually always a dedicated circuit.way2roll wrote:
Why do you say the house current isn't enough? I run a 50/30/15 adapter and plug it into an exterior house outlet. As long as I am careful to run one AC only, no problem. Seems like this is more complicated than it needs to be unless I am missing something.
House loads on that circuit. He not only has to count RV loads, he has to count house loads too.
โSep-07-2020 07:33 AM
Old-Biscuit wrote:enblethen wrote:
A NEMA 14-30 is a 30 amp 120/240 device. A standard 50 amp cord body style adapter will not plug into it as the neutral pin is not long enough.
This configuration is used for a dryer. It is four wire, two hots, neutral and ground.
I would suggest if not being used any longer would be to change it out to a fifty amp NEMA 14-50 receptacle, then use a standard 50 amp to 30 amp RV adapter.
If receptacle is needed for some other device, add another box and install a standard 30 TT receptacle. Connect one led of the circuit, neutral and ground. Insure it is wired 120 volts.
Do THIS^^^^^^^
Simple swap of receptacles
And be done with it!
โSep-07-2020 06:38 AM
eldel wrote:
I'd really like to be able to run the AC on my rig when I've got it parked outside the house before we take off on a trip. The 110V house supply isn't enough but I do have a 220V / 30A outlet in the garage which is a 14-30 outlet.
I'm looking and reading but I don't see anywhere where I can get a 14-30 to TT-30 converter. 14-50 to TT-30 yes. Is this even possible (assuming that the 14-50 converter just splits 220/50 into 2 x 110/25) or am I looking at wiring in a new circuit?
โSep-07-2020 06:13 AM
โSep-07-2020 06:12 AM
way2roll wrote:
Why do you say the house current isn't enough? I run a 50/30/15 adapter and plug it into an exterior house outlet. As long as I am careful to run one AC only, no problem. Seems like this is more complicated than it needs to be unless I am missing something.
โSep-07-2020 06:04 AM
โSep-07-2020 01:57 AM
โSep-06-2020 06:48 PM
pianotuna wrote:
coolmom,
Driers may be 240 volts. Be extremely careful.
โSep-06-2020 06:31 PM
โSep-06-2020 06:03 PM