โMar-23-2014 09:44 AM
โMar-25-2014 03:18 PM
Dusty R wrote:
There are check valves, both in and out on most water heaters, one of them is not allowing water into the water heater.
โMar-25-2014 05:02 AM
โMar-24-2014 06:22 PM
jeremywatco wrote:Old-Biscuit wrote:
The bypass valve is NOT used to 'temp' the hot water down.
Cold inlet valve should be wide OPEN & bypass fully CLOSED when WH is in service.
With the bypass cracked open the cold water line is connected to hot water line and the hot out check valve is being closed from cold water pressure.
You control water temp by mixing cold/hot at the faucet.
With bypass closed and no hot water flow.........check valve on hot outlet stuck closed.
Turn off water supply, open WH PRV to relieve pressure in tank and let water drain down in from top of tank.
Disconnect Hot outlet line
Inside the fitting on tank is a cheapo plastic plunger/spring/o-ring valve. Held inplace with a clip. Remove clip and internals. Then connect water line.
Turn on water supply...heat water........voila Hot water flow.
Then at you convenience install a shut-off valve in hot outlet lne and forget about that stupid check valve.
Got it, this makes perfect sense.
Is it normal for me to have much lower hot water pressure than cold water using water pump or city water? I'd say about 50-75% the flow
โMar-24-2014 05:57 PM
โMar-23-2014 12:20 PM
โMar-23-2014 10:11 AM
โMar-23-2014 09:58 AM