MySuncoastRV wrote:
A good method to test for propane leaks is to utilize your manometer at the stove by disconnecting the flute. The normal operating pressure should read between 10-15psi max. Bleed the pressure down to 3psi by opening the adjacent burner valve. Let the manometer sit idle for 3 minutes. If it remains at 3psi you have no leaks. Checking for leaks at full pressure is not advised as expansion of the gas could mask leaks at that pressure while using a monometer.
โAug-28-2018 12:37 PM
j-d wrote:
I notice some detectors specify "Natural Gas", others "LPG" and some specify Both.
Is this labeling or an actual difference in the detectors? We don't have "Gas" at home, so my only interest would be LPG for RV, BBQ, etc.
โAug-28-2018 08:42 AM
โAug-28-2018 08:36 AM
โAug-28-2018 08:28 AM
time2roll wrote:
Did the leak detector eventually pinpoint all the leaks? No soap and water?
โAug-28-2018 08:21 AM
โAug-28-2018 07:49 AM
Chris Bryant wrote:
What OB said. The national standard is 3 minutes with zero change, some states go to 15 minutes, which is what I always did. Pressure drop test every time the system is opened, and annually.
The thinking behind the three minutes is a leak that small will not result in a flammable concentration of lp. Also keep in mind the electric valves on all of the appliances actually have an "allowable" leak rate, very small, but allowed.