myredracer wrote:
Can't find furnace specs for that model. What does whatever info you have say it should be? Never, ever trust what an RV dealer tells you.
Mar-24-2016 11:30 AM
nebmike wrote:
So I pulled the rear panel off the unit -- its an SF-20FQ... which pisses me off because I specifically asked two different people at the dealership and was told it had a 30,000 btu furnace. 😕
Anyway, this is a 37' long camper with 3 slides -- is this just simply not enough furnace for me?
Mar-24-2016 10:56 AM
Mar-24-2016 08:18 AM
Mar-24-2016 07:23 AM
Mar-24-2016 06:44 AM
Mar-24-2016 05:53 AM
Mar-24-2016 05:35 AM
Mar-24-2016 05:15 AM
Mar-24-2016 05:03 AM
wasatchmtnatvr wrote:
Please post model number of furnace. This is important. Either furnace hitting high limit switch which cause an open circuit, which deletes power to circuit board, ceasing flame operation, and flame will shut off. When limit cools contacts close, causing power to circuit board, 24 seconds later, flame will re-appear. When this sequence occurs you feel cooler air than hot , but it will not be cool air. Cause, inadequate air flow usually caused by not enough heat discharge ducts for furnace to vent heat out, or breathe. If soft ducting you should have a minimum of 4 full size tubes coming off of furnace shell and registers fully open at discharge within interior. Virtually every furnace will work better if you can install an additional discharge warm air duct.