Jan-06-2018 07:25 PM
Jan-07-2018 10:20 AM
Bud
USAF Retired
Pace Arrow
Jan-07-2018 10:14 AM
ScottG wrote:I've often wondered about that too. Cost is around $40 retail. When it comes to residences, they now call for GFCIs and AFCIs on just about anything they can think of. The NEC code writers don't seem to pay the attention to the RV world it deserves.
Oddly, GFCI is not required by NEC for a "Trailer" 30A supply or even a RV 50A outlet.
Jan-07-2018 09:37 AM
Harvard wrote:
For the record, DC resistance readings will not detect stray capacitance leakage current (AC leakage).
Jan-07-2018 09:01 AM
Jan-07-2018 08:55 AM
enblethen wrote:
It does not take much o trip a GFCI receptacle.
OP: try unplugging your 120 volt cord powering your refer. Grounded heating element is a common item that goes bad and can trip GFCI.
Is the PI unit hardwired or does it have plug and receptacles. If it is plug and receptacle by-pass the unit. If it is hardwired and you have some experience wirte around the unit.
Jan-07-2018 08:52 AM
ktmrfs wrote:
If you have access to an DVM, measure the resistance between the neutral and ground on your trailer plug. It should read in the megohms. If it reads a few ohms, say 10 or less you have a ground neutral bond in the trailer. this is a NO NO. it is against NEC code, and it WILL trip an upstream GFI even if ALL the breakers in the trailer are turned off.
If it reads in the Kohms, but less than about 1 Megohm, you likely have some circuit with leakage to ground. again that can likely trip the GFI and you need to find the source of the leakage.
Since you said the OP installed the surge protector I would carefully check the surge protector wiring and any wiring in the trailer panel for any ground/neutral connection.
If resistance is in the meghom range, do as I previously suggested. turn off all breakers, plug into a GFI outlet, then turn on the 30A. if no trip, then turn on the other breakers one at a time till you trip. only have the 30A and ONE breaker on at a time.
And BTW, the electrician at the storage place is not much of an electrician. If he was he would know that an open ground will NOT trip a GFI. GFI's work just fine on circuits with NO ground. they still protect you and will not trip on an open ground.
In fact,other than checking for a ground/neutral short, a GFI does not even look at current in the ground lead. It looks for a difference between hot and neutral current. If there is a difference, that means there is current flowing in another circuit, like through your body, back to the voltage source.
Jan-07-2018 07:42 AM
Jan-07-2018 07:04 AM
Jan-07-2018 05:28 AM
Bud
USAF Retired
Pace Arrow
Jan-07-2018 04:56 AM
Jan-06-2018 09:26 PM
ScottG wrote:ktmrfs wrote:Tom/Barb wrote:DBECHEN wrote:
Hi all, I have been having a problem with plugging into the shore power at our storage facility. They have all circuits run through GFCI outlets on the pole. When we plug in and we are not running anything the GFCI trips on the pole. We talked to our storage facility manager and they had an electrician come out and he said the issue was our RV having an open ground. We have a Progressive Industries surge protector that was installed by the first owner. When we plug into the 30 amp plug at our house and in campgrounds there is no problem. Any ideas what may be causing this? Thanks in advance.
You do not tell us what Amperage you are plugged into at the storage facility.
GFI protection is very rare for 30 AMP circuits So, I'd assume you are reduced to a lower amperage circuit like 15 AMP or maybe a 25 AMP circuit.
And your Surge protector may be having a problem with it.
120V 30A GFI breakers are not very rare at all. maybe not many installed, but even lowes and home depot have them on the shelf. I had not trouble at all getting one when I installed a 120V 30A circuit for trailer power.
Oddly, GFCI is not required by NEC for a "Trailer" 30A supply or even a RV 50A outlet.
Jan-06-2018 09:25 PM
ScottG wrote:ktmrfs wrote:Tom/Barb wrote:DBECHEN wrote:
Hi all, I have been having a problem with plugging into the shore power at our storage facility. They have all circuits run through GFCI outlets on the pole. When we plug in and we are not running anything the GFCI trips on the pole. We talked to our storage facility manager and they had an electrician come out and he said the issue was our RV having an open ground. We have a Progressive Industries surge protector that was installed by the first owner. When we plug into the 30 amp plug at our house and in campgrounds there is no problem. Any ideas what may be causing this? Thanks in advance.
You do not tell us what Amperage you are plugged into at the storage facility.
GFI protection is very rare for 30 AMP circuits So, I'd assume you are reduced to a lower amperage circuit like 15 AMP or maybe a 25 AMP circuit.
And your Surge protector may be having a problem with it.
120V 30A GFI breakers are not very rare at all. maybe not many installed, but even lowes and home depot have them on the shelf. I had not trouble at all getting one when I installed a 120V 30A circuit for trailer power.
Oddly, GFCI is not required by NEC for a "Trailer" 30A supply or even a RV 50A outlet.
Jan-06-2018 09:23 PM
Tom/Barb wrote:ktmrfs wrote:
only if the house circuit is on a GFI. and in most houses GFI is on outside circuits, bathroom circuits, and kitchen circuits. a garage circuit usually is not on a GFI, so make sure you plug into a GFI Circuit.
All house circuits are on breakers, If there is a short in the trailer it will pop the breaker.
we know where the GFIs are required.
Jan-06-2018 09:21 PM
ktmrfs wrote:Tom/Barb wrote:DBECHEN wrote:
Hi all, I have been having a problem with plugging into the shore power at our storage facility. They have all circuits run through GFCI outlets on the pole. When we plug in and we are not running anything the GFCI trips on the pole. We talked to our storage facility manager and they had an electrician come out and he said the issue was our RV having an open ground. We have a Progressive Industries surge protector that was installed by the first owner. When we plug into the 30 amp plug at our house and in campgrounds there is no problem. Any ideas what may be causing this? Thanks in advance.
You do not tell us what Amperage you are plugged into at the storage facility.
GFI protection is very rare for 30 AMP circuits So, I'd assume you are reduced to a lower amperage circuit like 15 AMP or maybe a 25 AMP circuit.
And your Surge protector may be having a problem with it.
120V 30A GFI breakers are not very rare at all. maybe not many installed, but even lowes and home depot have them on the shelf. I had not trouble at all getting one when I installed a 120V 30A circuit for trailer power.
Jan-06-2018 09:19 PM
Tom/Barb wrote:DBECHEN wrote:
Hi all, I have been having a problem with plugging into the shore power at our storage facility. They have all circuits run through GFCI outlets on the pole. When we plug in and we are not running anything the GFCI trips on the pole. We talked to our storage facility manager and they had an electrician come out and he said the issue was our RV having an open ground. We have a Progressive Industries surge protector that was installed by the first owner. When we plug into the 30 amp plug at our house and in campgrounds there is no problem. Any ideas what may be causing this? Thanks in advance.
You do not tell us what Amperage you are plugged into at the storage facility.
GFI protection is very rare for 30 AMP circuits So, I'd assume you are reduced to a lower amperage circuit like 15 AMP or maybe a 25 AMP circuit.
And your Surge protector may be having a problem with it.