kearlms wrote:
Seems like a bunch of confusion about heating and AC. We will only is the furnace not a 1500 watt heater. AC is not even a consideration as out highs are fairly hitting mit to upper 60's. We also have a gen set if we need any big loads we will hook that up and get the 30 ampswe need. Hope this clears some things up.
Apr-21-2019 06:39 PM
drsteve wrote:myredracer wrote:
Sorry, but you clearly don't understand voltage drop in a branch circuit.
Yup... The outlet you plug the extension cord in to probably is not putting out 120V in the first place. To get a true idea of the voltage at the end of the cord, you need to know the real world voltage at the outlet. Not just the theoretical 120V number from the power company.
It's like using the brochure dry weight to figure out what you can tow.
Apr-21-2019 10:09 AM
myredracer wrote:
Sorry, but you clearly don't understand voltage drop in a branch circuit.
Apr-21-2019 08:45 AM
Apr-21-2019 08:12 AM
SoundGuy wrote:SoundGuy wrote:
The OP's original question was whether 100' of 12 gauge drawing from a 15 amp circuit would be suitable for his intended use and the answer is YES. Even assuming a maximum draw of 15 amps voltage drop over that 100' of 12 gauge would only be 4.76 volts.myredracer wrote:
What you are ignoring is the overall length of what the circuit could be. Is it 200', 250' or maybe 300'
Wrong again - the OP specifically said this cable run would be 100', drawing from a 15 amp source. This voltage drop calculator specifies "distance" as the one way distance from source to load. Obviously we have no way of calculating any further loss within the rig itself, nor does the OP - but the point remains that loss over 100' of 12 gauge even when drawing a full 15 amps is still well within acceptable limits.
Apr-21-2019 08:01 AM
Apr-21-2019 07:41 AM
SoundGuy wrote:
The OP's original question was whether 100' of 12 gauge drawing from a 15 amp circuit would be suitable for his intended use and the answer is YES. Even assuming a maximum draw of 15 amps voltage drop over that 100' of 12 gauge would only be 4.76 volts.
myredracer wrote:
What you are ignoring is the overall length of what the circuit could be. Is it 200', 250' or maybe 300'
Apr-21-2019 07:12 AM
myredracer wrote:SoundGuy wrote:
I'd go remeasure each of the 1/2 dozen electric heaters I own but guess what - I don't have to "back up" anything and frankly don't care whether you believe it, or not. 😛 FACT is, only one of my heaters that are labeled as "1500 watt" draws anywhere near that much, ALL the rest pull much less.
You muddied the waters by bringing up that heaters put out a fair bit less than their rating. I recommend reading the UL standard for portable electric space heaters which covers construction details, testing and labeling. Do you know what the OP's heater might put out?
The OP's original question was whether 100' of 12 gauge drawing from a 15 amp circuit would be suitable for his intended use and the answer is YES. Even assuming a maximum draw of 15 amps voltage drop over that 100' of 12 gauge would only be 4.76 volts.
What you are ignoring is the overall length of what the circuit could be. Is it 200', 250' or maybe 300' and how much is #14 ga? It's also important to take into account the starting voltage at the source. Not knowing either, nobody can assure that #12 is adequate for an extension cord - you cannot look at 100' of extension cord in isolation and assume that the starting voltage is 120 volts.
For example: Say the wiring in the house was 100' of #14 panel to plug (or whatever it is being plugged into), the extension cord is 100' of #12 and the shore power cord is 25' of #10, at a starting voltage at the source of 120 volts at a draw of 15 amps, the voltage would be down to 106.9 volts in the RV for a drop of 11%. Even then, that ignores what the wiring from the house's panel is to the street, how long and what gauge, which could (and sometimes does) affect voltage drop. I don't think the OP has provided adequate info. to make a definitive determination. If someone want to try and save $50 or so to take a gamble, that's up to them.
Apr-20-2019 07:43 PM
SoundGuy wrote:
I'd go remeasure each of the 1/2 dozen electric heaters I own but guess what - I don't have to "back up" anything and frankly don't care whether you believe it, or not. 😛 FACT is, only one of my heaters that are labeled as "1500 watt" draws anywhere near that much, ALL the rest pull much less.
You muddied the waters by bringing up that heaters put out a fair bit less than their rating. I recommend reading the UL standard for portable electric space heaters which covers construction details, testing and labeling. Do you know what the OP's heater might put out?
The OP's original question was whether 100' of 12 gauge drawing from a 15 amp circuit would be suitable for his intended use and the answer is YES. Even assuming a maximum draw of 15 amps voltage drop over that 100' of 12 gauge would only be 4.76 volts.
What you are ignoring is the overall length of what the circuit could be. Is it 200', 250' or maybe 300' and how much is #14 ga? It's also important to take into account the starting voltage at the source. Not knowing either, nobody can assure that #12 is adequate for an extension cord - you cannot look at 100' of extension cord in isolation and assume that the starting voltage is 120 volts.
For example: Say the wiring in the house was 100' of #14 panel to plug (or whatever it is being plugged into), the extension cord is 100' of #12 and the shore power cord is 25' of #10, at a starting voltage at the source of 120 volts at a draw of 15 amps, the voltage would be down to 106.9 volts in the RV for a drop of 11%. Even then, that ignores what the wiring from the house's panel is to the street, how long and what gauge, which could (and sometimes does) affect voltage drop. I don't think the OP has provided adequate info. to make a definitive determination. If someone want to try and save $50 or so to take a gamble, that's up to them.
Apr-20-2019 06:02 PM
Apr-20-2019 10:58 AM
pianotuna wrote:
So that 1500 watt heater puts out only 1,140 watts.
SoundGuy wrote:
Rarely does a so-called "1500 watt" electric heater actually draw 1500 watts, most often much less.
myredracer wrote:
I'd like to see a link from credible sources that can back that up.
Apr-20-2019 10:07 AM
Apr-20-2019 09:14 AM
pianotuna wrote:Tuna-man is right on the money. Most wholesalers sell to the public. Savings can be a LOT over retail. You can get quality commercial grade plugs and connectors that way too.
Hi,
Don't buy a premade cord. Go to an electrical wholesaler and purchase 100 feet of #10-3. Get the type rated for cold weather and UV resistant.
pianotuna wrote:
120 x 120 = 14,400
105 x 105 = 11,025
11,025 / 14,400 =~76% or a loss of 24% of wattage.
So that 1500 watt heater puts out only 1,140 watts.
SoundGuy wrote:I'd like to see a link from credible sources that can back that up. I tested several heaters a few years ago and got the rated output on the labels. If they don't, they aren't complying with the applicable UL/CSA standard. I'd like to see where in the UL standard it's okay not to provide the rated output. If the output is a lot less than the label, at 105 volts, they will put out waaay less than 1500 watts and be next to useless.pianotuna wrote:
So that 1500 watt heater puts out only 1,140 watts.
Rarely does a so-called "1500 watt" electric heater actually draw 1500 watts, most often much less. I've got a 1/2 dozen electric heaters of various types and only one comes anywhere near to drawing 1500 watts, one when running on HI draws a little over 900 watts despite the fact it's labeled as a "1500 watt" heater.