BurbMan wrote:
Haha glad you got it working! Bookmark the info, your circuit board is on borrowed time.... 🙂
Jan-04-2021 06:08 PM
Jan-04-2021 05:12 PM
Bud
USAF Retired
Pace Arrow
Jan-04-2021 03:09 PM
Jan-04-2021 11:47 AM
Jan-04-2021 10:52 AM
Jan-04-2021 10:29 AM
Old-Biscuit wrote:
Switch on furnace is dual purpose...It is On/Off for using when working ON the furnace (turn it off then it can't start accidentally)
It also is a Circuit Breaker that can trip if high amp load is sensed when using furnace
Normally that switch should be ON & Reset
Thermostat is the 'switch' that turns furnace ON
Set thermostat to HEAT Mode, Turn set point above room temp and you should hear thermostat 'CLICK' then shortly after you should hear Furnace FAN start
Atwood Furnace Service Manual
Pg 8 ---wiring diagram ---yours would be thr one on right or bottom one (2001 Vintage used a Timed Delay Relay)
Pg 16 lists Sequence of Operation
Pg 22 has break down of furnace components
Pg 29 Troubleshooting
Pg 39 Exploded View
Pgs 49-52 Part Numbers
Jan-04-2021 10:11 AM
Jan-04-2021 09:54 AM
enblethen wrote:
Yes, without thermostat, the furnace is not told to come on.
Switch is there for maintenance safety. Turning it off shuts down furnace power so it doesn't come on when your fingers are in it.
Jan-04-2021 09:25 AM
Bud
USAF Retired
Pace Arrow
Jan-04-2021 08:29 AM
enblethen wrote:
Make and model of furnace?
What is thermostat set at?