phemens wrote:
Every wire gauge calculator I've tried recommended 4/0 cable for my setup, and my lengths are nowhere near 30ft. From the battery bank to the bus bars is 3ft, and from the bus bars to the 3000 W inverter is 5ft. At 300 amps for a couple of minutes (say running the microwave), those wires heat up fast. I'm not going to gamble an expensive set of batteries for a couple of bucks.
โJan-24-2021 04:42 PM
RickLight wrote:
Yeah we can get off track easily.
Sounds like the big question is how much better will the solar be with shorter wires? Longer 120 is not a factor under 50'.
Plan exclusively for the future 400W system. Then do your voltage drop calculations for both ways. https://www.southwire.com/calculator-vdrop At 10' 6AWG is probably good, but 4 will be half the loss. What can't be calculated is the value of your cash and sweat.
Moving LI batteries inside is a no brainer for me, if you plan on any cool temps. I've been snowed on in mid summer! There are heaters for batteries but that takes time with the truck noise, fuel and fuss.
โJan-24-2021 04:34 PM
Bert the Welder wrote:
Just saw a LiFePo battery that has a warmer built in. It seems to kick on first, before putting the juice to the cells. Once warm, the BMS lets the charge go through. CanBat was the company. Canadian, eh.....
โJan-06-2021 05:56 AM
Grit dog wrote:IMO one should strive for =<2% of voltage drop (while under maximum load) to get maximum productivity from the inverter and battery. Higher voltage drops reduce the number of AH you can access from the battery, and thus the inverter's runtime.
My mistake, by much smaller, I meant couple sizes (which is considerably smaller diameter and cost).
A 2000W inverter will draw approx 200A at full load.
I also assumed a relatively short wire run, under 10โ. With that 1/0 would be more than sufficient and 2/0 would be conservative.
No harm in overkill on wire size. ( Just like pickup trucks, right? Lol). Just not necessary for the load from a 2000W inverter unless itโs a long run. Which would make no sense as itโs far more efficient to have the DC load close to the power source and distribute with AC current to AC loads.
โJan-06-2021 03:56 AM
StirCrazy wrote:Grit dog wrote:
^Like I said, no harm, no foul. Iโm sue your setup works great.
Itโs just not necessary to use wire that size.
Starter motor on a diesel pickup pulls 450+ amps through 2/0 wire, for comparison.
More so posted for others who donโt have the knowledge, that they do not think 4/0 welding cable is required for this setup.
Cheers
Happy New Years !
wow, I dont know if I would use 4/0 for anything but welding haha. I dont have a situation where I have to carry 400plus amps up to 30 feet away. but ya if you got it use it.
Every wire gauge calculator I've tried recommended 4/0 cable for my setup, and my lengths are nowhere near 30ft. From the battery bank to the bus bars is 3ft, and from the bus bars to the 3000 W inverter is 5ft. At 300 amps for a couple of minutes (say running the microwave), those wires heat up fast. I'm not going to gamble an expensive set of batteries for a couple of bucks.
โJan-05-2021 10:17 AM
โDec-29-2020 03:36 PM
Grit dog wrote:
^Like I said, no harm, no foul. Iโm sue your setup works great.
Itโs just not necessary to use wire that size.
Starter motor on a diesel pickup pulls 450+ amps through 2/0 wire, for comparison.
More so posted for others who donโt have the knowledge, that they do not think 4/0 welding cable is required for this setup.
Cheers
Happy New Years !
โDec-29-2020 07:11 AM
โDec-28-2020 04:43 PM
Grit dog wrote:PastorCharlie wrote:
When installing my system I used 4/0 welding cable with equal runs connecting 4 batteries ( 450 ah ) and a 2,000 watt Magnum inverter. Fuse the + at battery. All terminals are both crimped and soldered. Estimate your needed run and buy the cable in one piece and cut to desired lengths. Simple and minimizes loss.
4/0? OMG, why?
Presume you had it laying around and then thus more economical than buying adequate but much smaller cable?
โDec-28-2020 09:26 AM
โDec-28-2020 08:10 AM
Grit dog wrote:PastorCharlie wrote:
When installing my system I used 4/0 welding cable with equal runs connecting 4 batteries ( 450 ah ) and a 2,000 watt Magnum inverter. Fuse the + at battery. All terminals are both crimped and soldered. Estimate your needed run and buy the cable in one piece and cut to desired lengths. Simple and minimizes loss.
4/0? OMG, why?
Presume you had it laying around and then thus more economical than buying adequate but much smaller cable?
โDec-28-2020 07:30 AM
โDec-27-2020 02:19 PM
PastorCharlie wrote:
When installing my system I used 4/0 welding cable with equal runs connecting 4 batteries ( 450 ah ) and a 2,000 watt Magnum inverter. Fuse the + at battery. All terminals are both crimped and soldered. Estimate your needed run and buy the cable in one piece and cut to desired lengths. Simple and minimizes loss.