Dedicated Outlet

CabinetmakerII
Explorer
Explorer
We like cook to outside to minimize the associated mess inside the coach. More often than not, we would end up tripping a circuit breaker inside the coach. My wife asked if there was a way to install a separate circuit to prevent tripping the breakers. There was space within the breaker panel for an additional breaker and after a bit of looking I decided to place the dedicated 20 amp circuit inside the basement within easy reach with an extension cord. I purchased all the necessary supplies from the local hardware store (only one trip!) and had the outlet installed in about two hours. Now when we cook or have other electrical needs outside we can do so without worry of tripping other breakers.
Cabinetmaker

2021 DRV 39 DBRS3
2017 F-450 4X4, Riece 24K Hitch
2011 F-450 4X4, Companion 18K Hitch, Air Bags (Retired)
2012 Cyclone 3800, 5th Airborne Kingpin (Retired)
2018 Polairs 1000 XP Side by Side
12 REPLIES 12

Y-Guy
Moderator
Moderator
Cabinetmaker the extra circut makes sense, kudos on wiring it up and solvign yoru issue.

Another thing for all of us to check is how they wire the plugs. Most often they backstab the wire into the electrical outlet. In a home that isn't moving it might be ok (not my preference) but in an RV this can be a much bigger issue. I had issues with a couple of mine popping breakers. When I went through the RV and changed from backstab to twist the wire around a screw and I stopped having issues.

It's also helpful to know which plug are on the circuit and which are tied into a GFI outlet.

Two Wire Fox Terriers; Sarge & Sully

2007 Winnebago Sightseer 35J

2020 Jeep Gladiator Rubicon

CabinetmakerII
Explorer
Explorer
2oldman wrote:
Ok.. I would have suggested running another cord to the pedestal. Most have multiple outlets.


The lot we "Winter" on has only a 50 amp connection at the pedestal. Also an issue when dry camping running the gen set. Now there is no worries about turning on the microwave or anything else when cooking outside with an electric skillet.
Cabinetmaker

2021 DRV 39 DBRS3
2017 F-450 4X4, Riece 24K Hitch
2011 F-450 4X4, Companion 18K Hitch, Air Bags (Retired)
2012 Cyclone 3800, 5th Airborne Kingpin (Retired)
2018 Polairs 1000 XP Side by Side

Dirtclods
Explorer
Explorer

pianotuna
Nomad III
Nomad III
Another idea for the kitchen area is to add a dedicated inverter powered outlet. That gets me around the 1 appliance limit.

I do have the OEM 30, 20 and 15 amp shore power cords. It works well for me.
Regards, Don
My ride is a 28 foot Class C, 256 watts solar, 556 amp-hours of Telcom jars, 3000 watt Magnum hybrid inverter, Sola Basic Autoformer, Microair Easy Start.

Happy_Prospecto
Explorer
Explorer
Good idea CabinetmakerII, glad it's working for you.
Kevin
Retired, Fulltime RV'er, 1999.5 F350 4X4 CC Diesel Flatbed
2007 Alpenlite Defender Toyhauler, 2019 Polaris Ranger
Bob, the Yorkie Terrier helping me prospect til the money runs out

rockhillmanor
Explorer
Explorer
It's just a matter of getting used to not turning on two appliances on at the same time. Which IMHO does not in any way restrict your use of the RV.

Almost all of us when we get our first RV we are tripping breakers left and right. Then over time you get in the habit of making sure not to use 2 major appliances at the same time and the constant tripping of breakers goes by the wayside. :C

We must be willing to get rid of the life we've planned,
so as to have the life that is waiting for us.

bob213
Explorer
Explorer
You are still limited by the max amp. of your trailer. 2oldman's suggestion would be separate from the load on your coach.
You can avoid reality, but you cannot avoid the consequences of avoiding reality – Ayn Rand

Dirtclods
Explorer
Explorer
Here's a good chart as well


http://www.diybyexample.info/2010/07/what-size-extension-cord-do-i-need/
AAA Motorcycle RV Plus

CA_Traveler
Explorer III
Explorer III
Good plan. Now install a inside circuit that plugs into your new storage plug. I use mine to plug into a second pedestal plug with an extension cord for additional inside ceramic heaters when I'm on 30A. So I have 30A + 20A.
2009 Holiday Rambler 42' Scepter with ISL 400 Cummins
750 Watts Solar Morningstar MPPT 60 Controller
2014 Grand Cherokee Overland

Bob

RoyB
Explorer II
Explorer II
I run a multi-tap extension cord from the 20AMP Pedestal connection to our patio area to use. This does not draw from the 30AMP Connection feeding the trailer...

Similar to this one from google search...



Roy Ken
My Posts are IMHO based on my experiences - Words in CAPS does not mean I am shouting
Roy - Carolyn
RETIRED DOAF/DON/DOD/CONTR RADIO TECH (42yrs)
K9PHT (Since 1957) 146.52M
2010 F150, 5.4,3:73 Gears,SCab
2008 Starcraft 14RT EU2000i GEN
2005 Flagstaff 8528RESS

enblethen
Nomad
Nomad
2oldman has the right idea.
Hopefully you installed a GFCI receptacle!

Bud
USAF Retired
Pace Arrow


2003 Chev Ice Road Tracker

2oldman
Explorer II
Explorer II
Ok.. I would have suggested running another cord to the pedestal. Most have multiple outlets.
"If I'm wearing long pants, I'm too far north" - 2oldman