Water-Bug wrote:I stand corrected. Must have had a brain fart.Bird Freak wrote:john&bet wrote:I may be wrong but I don't think this is right. I believe a 50 amp plug has 2 neutral's and 2 hot's and a ground both hots are 50 amp. If so than you will only pull 30 amps from each 50 amp lead if your plug just splits to 2 30 amp plugs.
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
X2
An RV 30 amp circuit has a single 30 amp leg or app 3000+ watts capacity. An RV 50 amp circuit has 2 ea 50 amp leg of app 5000+ watts each for a total of 10, 000+ watts.
EDIT The 50 amp RV circuit has 2 hot, 1 neutral and 1 ground pins.
โJan-08-2014 05:57 PM
โJan-08-2014 05:56 PM
john&bet wrote:
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
โJan-08-2014 04:27 PM
john&bet wrote:
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
โJan-08-2014 04:04 PM
john&bet wrote:
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
โJan-08-2014 03:54 PM
Bird Freak wrote:john&bet wrote:I may be wrong but I don't think this is right. I believe a 50 amp plug has 2 neutral's and 2 hot's and a ground both hots are 50 amp. If so than you will only pull 30 amps from each 50 amp lead if your plug just splits to 2 30 amp plugs.
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
โJan-08-2014 03:29 PM
john&bet wrote:I may be wrong but I don't think this is right. I believe a 50 amp plug has 2 neutral's and 2 hot's and a ground both hots are 50 amp. If so than you will only pull 30 amps from each 50 amp lead if your plug just splits to 2 30 amp plugs.
The safety of the idea has not been address yet so let me be the first. You have the potential to overload the neutral of the adapter or the neutral of the recptical or the neutral anywhere up stream of that point. If both 30 amps are loaded to say 24 amps then there is 48 amps on the neutral which will be pushing it and the connections. JMHO.
โJan-08-2014 03:18 PM
โJan-08-2014 03:13 PM
โJan-08-2014 02:57 PM
โJan-08-2014 01:18 PM
Old-Biscuit wrote:
YEP..........LINK
โJan-08-2014 01:13 PM
โJan-08-2014 01:10 PM