Ok, have a quick question for you electrical guys. I had to pull my Onan 4000 generator for some landing gear work. Noticed that the AC feed wires are 12 gauge and about 6' long before a junction box where they tie into 10 gauge wire to run back to the converter. I understand that the generator has a 30A breaker on the control panel, so it won't ever put out more than 30A. I thought that 12 ga wire was too small for a 30A circuit, but that is what came on it from Onan. Should I rewire with 10 gauge or just trust that Onan knows what they're doing??
2006 Chevrolet Silverado 2500HD CCSB Duramax/Allison
2012 Puma Unleashed 356QLB FWTH
39 REPLIES 39
RJsfishin
In this calculator, I just punched in 30 amps, 120 volts, at 4 ft one way......came up 14 ga copper.
12 ga overkill ?
"Battery Salesman", quit snibblin, change the charts, maybe go back to sellin batteries !
http://www.csgnetwork.com/wiresizecalc.html
Rich
'01 31' Rexall Vision, Generac 5.5k, 1000 watt Honda, PD 9245 conv, 300 watts Solar, 150 watt inv, 2 Cos 6v batts, ammeters, led voltmeters all over the place, KD/sat, 2 Oly Cat heaters w/ ox, and towing a 2012 Liberty, Lowe bass boat, or a Kawi Mule.
dougrainer
MEXICOWANDERER wrote:
Try as I might, I have looked at hundreds of Onan generators, and not a one had umbilical wire sticking out of it. Must be a conspiracy between Onan and the vehicle manufacturer, huh?
Onan used to use a phenoic terminal block for OEM to connect to right inside the control box. Big gensets like >1MW used Kerny Nuts that did not come with the genset. Onan's liability ended at these terminations. Yotta try confronting a 12-wire connection that runs through a Scott Connection pair of transformers.
New RV manufacturers would be glad to hear from you if you could reach someone who speaks English.
Just for MECHANICAL STRENGTH alone I would hesitate to use 12 gauge on an 30-amp circuit. Even six-inches.
RV Onan Gensets come with the 120 wire harness attached from Onan. The length of that harness (some are 3 wire and some are 4 wire depending on the Genset), is about 6 foot. THIS 120 wiring is then connected to the RV at a 4x4 or 6x6 junction box. Then the RV OEM runs the 120 wiring from THAT box to the RV connections. In some installs the Genset is located close to the Transfer box or the 30/50 amp receptacle if no transfer box is used. In this case, the Onan is wired direct with no junction box. The wire Onan installs is within Code. Doug
Chris_Bryant
Just looked at the cutoff from the last Onan 7kw I installed- it is marked:
12 AWG (3.31mm2) E137925-L (UL) SIS 600V AND AWM 3173 600V OR 3237 1000V -- CSA CL1251 125C 600V OR AWM T A/B 125C 600V FT2 -- MADE IN USA
Other markings are LOAD CB1 | LOAD CB2 | NEUTRAL |and GND
This wire is from the factory- the only gensets I have run in to with lug hookups are the 33kw Kohler and the 45kw Onan I used to use.
-- Chris Bryant
RJsfishin
Doesn't matter what the wannabees and "the battery salesman" want to believe. according to the chart I saw (link won't post) 14 ga wire will carry 30 amps to 4ft long.
If ya don't like it, quit snibblin like little kids, and change the charts
Rich
MEXICOWANDERER
enblethen
An engineered system must have proper maintenance.
It is not to be used to circumvent the NEC.
Bud
USAF Retired
Pace Arrow
2003 Chev Ice Road Tracker
NinerBikes
enblethen wrote:
A full engineered system must also have proper maintenance personnel. It is not just a blanket engineered design so it is OK not to follow the NEC.
Please don't use double negatives in one sentence... try rephrasing the last sentence with no negatives, so we know what you mean.
enblethen
Bud
USAF Retired
Pace Arrow
RCMAN46
john&bet wrote:
RJsfishin wrote:
14 ga will carry 30 amps up to 4 ft
12 ga will carry 30 amps up to 8 ft.
Don't need no wannabe elect tech to tell you,...just look at a chart w/ ga and amps, and length of wire,
Oops, excuuuuuuuuse me, 12 ga will carry 30 amps for only 6 ft
This will probably get me booted, but here goes. You are completely wrong. The NEC says that you can not use a 30amp c/b on 12awg. Period. And 10awg can not have a c/b larger than a 30amp. Oh, and by the way I am not a "wannabe electrician" as you call some people. Statements like yours get me rialed up.
"The NEC says that you can not use a 30amp c/b on 12awg. Period."
Not correct. As I stated previously an engineered system does not fall under the requirements of the NEC. It is not uncommon to find wire sizing and circuit breaker sizing that does not meet NEC requirements in engineered/designed systems.
NinerBikes
Rj's fishing alright... he's trolling. I don't waste my time quoting him.
IMHO... some folks posts around here, I heavily discount. Apply information from outliers suggestions from most posts at your own peril. Or ask for their professional qualifications.
Critical thinking skills should be applied to all posts, and all posters, for trend analysis.
Bob_Landry
One of the things that amaze me about these electrical threads is that someone hasn't been killed following some of the advice given on here.
Another amazing thing is how many people give advice on wire size and don't even know that wire size for AC and DC are figured differently. I guess it really doesn't matter here as long as everyone gets to post something.
2011 Keystone Outback 277RL
john_bet
2018 Ram 3500 SRW CC LB 6.7L Cummins Auto 3.42 gears
2018 Grand Design 337RLS
RJsfishin
Quote:
It's working fine and is how Onan built it, so I re-installed it without changing anything
Smart move.
Hard to understand why you questioned an ONAN OEM factory installation in the first place.
And even harder to understand or believe is how many xxxxxxx here told you to change it !! Not smart.
Rich
enblethen
Just for info, Some rigs have the transfer switch mounted to the back of the converter.
Bud
USAF Retired
Pace Arrow