nowgrn4 wrote:I'm assuming you probably had the older, 8xx series, 13.5k BTU Coleman Mach III Power Saver. LRA was approx. 58a on these earlier generation models. The current 9xx series has a much lower LRA of 50a. This 8a reduction in LRA significantly improves the EU2000i's chance of successfully starting it with the Eco mode on.
I ran a 13.5K Coleman Mach III PS (power saver) for years with a Honda 2000. Many times boondocking in the summer down here for as long as a week running like this. I found running the thermostat on its coldest setting so the compressor never cycled off was the best policy. Pulling 8.3 AMPS continuously as indicated by the Kill-O-Watt meter. If it got too cold inside we would crack a window. Of course fridge would be set on propane and running electric griddle, coffee maker or microwave the A/C would be shut down.
โOct-07-2015 04:32 AM
โOct-01-2015 02:52 PM
otrfun wrote:
For those who would like to get past the many anecdotal, doomsday comments about running a 13.5k BTU a/c with one EU2000i, these two steps may help you gain a more objective perspective on the actual risk and chance of success:
1. Check the LRA (locked rotor amp) rating for your current or prospective 13.5k BTU a/c unit. If it's 50a or lower, odds are very high you can reliably start it with one EU2000i with the Eco mode on. Almost a sure thing with the Eco mode off. Once you're reasonably confident you can start it, now you can focus on step 2, running it.
2. Check the continuous current rating of your current or prospective 13.5k BTU a/c unit. Typically, the continuous current rating for the vast majority of 13.5k BTU a/c's range from 10-14a. Honda says the EU2000i can reliably provide 13.3a of current indefinitely, and 16.6a for up to 30 minutes. Assuming the LRA (from step 1) is low enough to allow reliable starts, and you trust Honda, then it's reasonable to assume one EU2000i has sufficient continuous power to reliably run the vast majority of 13.5k BTU a/c's.
Ok, so you don't trust Honda? Have a low tolerance for risk? Well, you do have the option of making life kinder and more gentler for your EU2000i. Simply purchase/use a 13.5k BTU a/c that has a continuous current rating much closer to 10a (along with a sufficiently low LRA).
If you're uncomfortable pushing your EU2000i to 10a, well, you may want to reconsider that drive to work this morning . . . I've heard it can be potentially fatal.
โOct-01-2015 02:32 PM
โOct-01-2015 01:04 PM
2oldman wrote:I'm sure everyone here would agree "all situations are different". Beyond that all bets are off.otrfun wrote:I would concede that.
His inefficient Dometic 13.5k BTU a/c would NOT start unless two (2) EU2000i's were run paralleled with the Eco mode OFF! It's a HUGE con when you have to run two EU2000i's with the Eco mode off---NOT quiet!
All situations are different. My DuoTherm Brisk Air starts and runs just fine with 2 paralleled 2ks on Eco mode. And I can run many things at the same time, including the MW for a minute or so, but they are definitely screaming at that point.
โOct-01-2015 12:19 PM
otrfun wrote:I would concede that.
His inefficient Dometic 13.5k BTU a/c would NOT start unless two (2) EU2000i's were run paralleled with the Eco mode OFF! It's a HUGE con when you have to run two EU2000i's with the Eco mode off---NOT quiet!
โOct-01-2015 12:15 PM
samsontdog wrote:Sound about right.
My EU2000 Honda would start and run my 13,500 A/C in my 2012 TT at Lake Tahoe.
I sold the gen and bought a EU3000 Honda G. The 3,000 would run for a while then bough down. Sold it and bought two Hondas EU2000 which run everything fine
โOct-01-2015 12:13 PM
โOct-01-2015 11:54 AM
2oldman wrote:It all depends how you define easier.otrfun wrote:Wouldn't it be much easier to purchase another 2000?
Well, you do have the option of making life kinder and more gentler for your EU2000i. Simply purchase/use a 13.5k BTU a/c that has a continuous current rating much closer to 10a (along with a sufficiently low LRA).
โOct-01-2015 11:08 AM
โOct-01-2015 10:55 AM
โOct-01-2015 10:22 AM
โOct-01-2015 09:56 AM
MrWizard wrote:Calicajun wrote:
Takes about 3,200 watts to tun an A/C unit.
where in the word did you get that number ?
12.5 amps times 120v, roughly 1800w to run an A/C unit
3200w would be about 26 amps at 120v
โOct-01-2015 09:53 AM
otrfun wrote:Wouldn't it be much easier to purchase another 2000?
Well, you do have the option of making life kinder and more gentler for your EU2000i. Simply purchase/use a 13.5k BTU a/c that has a continuous current rating much closer to 10a (along with a sufficiently low LRA).