Generator Jim wrote:
Last time I checked, Tampa Armature Works was charging well over two grand for the rotor.
โNov-05-2013 05:54 AM
โNov-04-2013 10:41 AM
vacuumbed wrote:
Here is the model #
6.5 NH-3CR/16004K
โNov-04-2013 09:10 AM
โNov-04-2013 04:18 AM
โNov-04-2013 03:23 AM
โNov-03-2013 11:28 PM
โNov-03-2013 07:51 PM
Generator Jim wrote:
134 vac is a little high. If you have a frequency (Hertz) meter, connect it across the 120 volts and adjust the governor speed spring on top of the cooling fan for 62 at no load and 58 at full load. Your voltage should be within tolerances at that point.
JimL
Scott and Sherrie -- where have you been, I missed you.
โNov-03-2013 07:21 PM
TEXAS wrote:
Since you have voltage. No damage was done. If the engine is going up and down. That would cause your voltage swing most of the time. Do as Jim says and you will be ok.