โOct-05-2018 02:56 PM
โOct-05-2018 08:34 PM
Teamfour wrote:I'm curious if you read the rest of my post where I explained why it wasn't correct? If the EMS doesn't have its own independent connection to ground (which it doesn't), it cannot positively diagnose an open ground. The EMS is sensing the lack of a neural-ground bond, and if it's not present, it assumes the fault is an open ground, when it in fact has no way of determining if that assumption is correct or not. In the floating output generator situation, you could drive the world's best ground rod, positively connect it to the EMS, and it will still say "open ground".road-runner wrote:
The "open ground" diagnosis is not correct.
The open ground diagnosis is correct. Straight from the folks who make the EMS:
โOct-05-2018 07:02 PM
โOct-05-2018 05:38 PM
โOct-05-2018 04:38 PM
โOct-05-2018 04:34 PM
Bud
USAF Retired
Pace Arrow
โOct-05-2018 04:24 PM
โOct-05-2018 04:13 PM
road-runner wrote:
The "open ground" diagnosis is not correct.
โOct-05-2018 03:56 PM
โOct-05-2018 03:46 PM
โOct-05-2018 03:34 PM
wnjj wrote:185EZ wrote:
I wanted a generator so I wouldn't have to run my 7000kw in the rv just to charge the batteries and run a few things.
Amazing what you can get for $250 these days
I have a Durastar 4400 generator but the hz would vary too much and it would trip error codes on my Progressive EMS and i couldn't just plug it into the rv since it would give a fault code on my inverter.
So I bought a dual fuel Sportsman
https://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936http://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936
Works great on propane and the hz only varies from 61 to 62 hz
But the EMS shows an error code of open ground.
I even tried grounding the terminal lug into the ground and nothing changed
Everything works fine if I bypass the EMS
What else can I do to fix the open ground?
You need to connect the ground pin to the neutral pin using a bonding plug at the generator or bypass your EMS when on generator power. You can probably bond one of the 20A outlets and it will suffice.
โOct-05-2018 03:16 PM
โOct-05-2018 03:06 PM
185EZ wrote:
I wanted a generator so I wouldn't have to run my 7000kw in the rv just to charge the batteries and run a few things.
Amazing what you can get for $250 these days
I have a Durastar 4400 generator but the hz would vary too much and it would trip error codes on my Progressive EMS and i couldn't just plug it into the rv since it would give a fault code on my inverter.
So I bought a dual fuel Sportsman
https://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936http://www.amazon.com/Sportsman-GEN4000DF-SS-Sandstorm-4000-Generator/dp/B079RBD936
Works great on propane and the hz only varies from 61 to 62 hz
But the EMS shows an error code of open ground.
I even tried grounding the terminal lug into the ground and nothing changed
Everything works fine if I bypass the EMS
What else can I do to fix the open ground?