I know there are newer campers that have combined water heater / furnace units but they are pricey and not necessarily an easy drop in unit. It got me to thinking that it would be an interesting experiment to see if a standard RV water heater and add furnace capability.

Pros:

1. Elimination of one large and complex component

2. Opening up space for additional storage

3. Possibly less heating hot/cold "cycles" at night because heated water in the tank would act as a stored reservoir of heat for the furnace.

4. Possibly quieter overall (my furnace is very noisy while my water heater is nearly silent).

Cons:

1. May take longer to heat interior

The idea I was thinking about is cutting access into the stainless water tank, running some stainless tubing channel inside with inlet connection and one outlet connection. Weld it all back together. Then running a line to a radiator / fan combination that ties into the existing ducting. Cycle the fluid with a water pump and use some sort of relay to activate the water pump with the fan when the thermostat calls for heat.

Aside from the welding, I don't see this as something too difficult. I know there are some very skilled people on this forum and so I am wondering if others have toyed around with the idea themselves.

This post is about whether the idea is feasible and could be done readily enough by a moderately skilled person. I'm not actually considering actually doing it (too many irons in the fire as it is) but might keep it in mind for a future project.

1999 F350 Dually with 7.3 Diesel
2000 Bigfoot 10.6 Camper
24 REPLIES 24

Grit_dog
Navigator
Navigator
Good idea until you use up your water and it gets cold that night.
2016 Ram 2500, MotorOps.ca EFIlive tuned, 5โ€ turbo back, 6" lift on 37s
2017 Heartland Torque T29 - Sold.
Couple of Arctic Fox TCs - Sold

ajriding
Explorer II
Explorer II
Recirculating the cold water from the (cold) hot water line back to the tank before the hot water gets to shower head is a big deal for most campers to save water, esp boondockers. This is a more critical point for me.
I just got used to taking cold showers in Spring and summer. After the first two it is no big deal, think about you washing your hands in cold water without discomfort. Saves water, but also saves huge amt of propane so I can go over a month on one 20lb tank just using for fridge and stove.
I dont use oven, heater or boiler anymore - creature comforts and big users of resources.
Tis not for everyone I know.
How did you that did, reroute/recirculate the water back in? Seems easy enough, but Im interested in the final version.

S_Davis
Explorer
Explorer
These could be made to work, they draw about .55 amps on high speed.http://www.turbonicsinc.com/kickster#specScroll

S_Davis
Explorer
Explorer
Like I said before make sure you don't run at condensing temperatures, you will rot the tank out in short order. I have seen hundreds of systems like you are describing and most of them the water heater was shot. I am a HVAC contractor with 26 years specializing in boiler and hydronic heating.

SidecarFlip
Explorer III
Explorer III
Having said that I don't believe it would work with a Suburban HWH because of the sacrifical anode gumming up the HX but an Atwood with no anode rod, certainly.

In retrospect, I've never been fond of the suburban design just because of the anode, a cheap way to cut cost over a porcelain line tank like the Atwood, I always have to flush the crud from the anode rod from mine every year as it drops to the bottom of the tank. Cheaper is always the by-line in RV's.
2015 Backpack SS1500
1997 Ford 7.3 OBS 4x4 CC LB

SidecarFlip
Explorer III
Explorer III
JD5150 wrote:
adamis wrote:
JD5150 wrote:
I have worked around air to water heat exchangers most of my life. Hot air from engine exhaust blowing on a stainless or copper coil to heat water at 600 psi around 2 gallons or more a minute.

The idea you have most likely will not work. Someone mentioned that a 12 gallon RV water heater is around 12,000 btu. So lets say a 6 gallon one is 6,000 btu. By the time you use air flow/fan to blow the heat you will be down to 3,000 btu or less. The fan will cool the air some so there will be some loss of heat there from fan picking up cooler air and blowing through the radiator coil.

I just started looking at the Truma Combi eco plus. I'm still studying it to see how much juice it will take to run in electric and gas mode. I want to run it off solar and a 200 amp hour lithium battery pack plus gas if needed. It will do both at the same time


The lower BTU output actually works to my advantage in this scenario. An Atwood 8 Gallon water heater is 8,800 BTUs, an Atwood Furnace is 35,000 BTUs. I don't need 35,000 BTUs constantly, there is a cycle time involved or I will be cooked out of the camper. Having a constant 8,800 BTUs burning with a lower fan speed and lower overall heat level but over a longer running time can have the equivalent effect as a blast furnace running for shorter periods of time.

Lower BTU then it should work. Are you going to use a 12 or 110 volt pump to move the water through the heat exchanger? If so you can find pumps that can handle 140 degrees without damage. There are very few that can handle 180 degrees without damage.


The TACO IFC circulator in my shop PEX system will handle up to 210 degree fluid (which can be water or Glycol), no problem but it's 110 volt. However the amp draw is very low (like 60 watts in the high position and 15 watts in the low position. You could run it from a PSW inverter and run on 12 volts, no issue.

I could see circulating hot water from the HWH no problem through a fluid to air HX with a fan behind it, installed in the cavity where the existing furnace is now. Would be a fairly cheap install and add a t'stat to cycle the pump and fan. No mods to the HWH at all, other than a return line to the HWH for cooled water and let the HWH maintain the tank temp. Has some interesting aspects so long as the HWH can keep up with the demand.
2015 Backpack SS1500
1997 Ford 7.3 OBS 4x4 CC LB

JD5150
Explorer
Explorer
adamis wrote:
JD5150 wrote:
I have worked around air to water heat exchangers most of my life. Hot air from engine exhaust blowing on a stainless or copper coil to heat water at 600 psi around 2 gallons or more a minute.

The idea you have most likely will not work. Someone mentioned that a 12 gallon RV water heater is around 12,000 btu. So lets say a 6 gallon one is 6,000 btu. By the time you use air flow/fan to blow the heat you will be down to 3,000 btu or less. The fan will cool the air some so there will be some loss of heat there from fan picking up cooler air and blowing through the radiator coil.

I just started looking at the Truma Combi eco plus. I'm still studying it to see how much juice it will take to run in electric and gas mode. I want to run it off solar and a 200 amp hour lithium battery pack plus gas if needed. It will do both at the same time


The lower BTU output actually works to my advantage in this scenario. An Atwood 8 Gallon water heater is 8,800 BTUs, an Atwood Furnace is 35,000 BTUs. I don't need 35,000 BTUs constantly, there is a cycle time involved or I will be cooked out of the camper. Having a constant 8,800 BTUs burning with a lower fan speed and lower overall heat level but over a longer running time can have the equivalent effect as a blast furnace running for shorter periods of time.

Lower BTU then it should work. Are you going to use a 12 or 110 volt pump to move the water through the heat exchanger? If so you can find pumps that can handle 140 degrees without damage. There are very few that can handle 180 degrees without damage.

Larry-D
Explorer II
Explorer II
Been done by some on the RPod forum but they didn't delete the furnace. Used a radiator/heat exchanger plumbed into the water heater's hoses.

adamis
Nomad II
Nomad II
toddb wrote:
I built a hydronic system in my old toy hauler. I started out using the water heater and then switched to a stand alone atwood water heater filled with glycol. It worked amazingly well, camped often to freezing and it maintained 65 in the trailer with a 50% duty cycle. The output was 140*, was really quiet, and didn't dry out the air in the trailer.

I'm currently collecting parts to utilize the water heater in the TC. Using the water in the tank is a bad idea, the anode crude plugs everything up. My plan is to pull the water heater and wrap a coil around it, topsflo circulation pump and 120mm fan/pc radiator. We use a use a similar setup at work to cool compressor heads, not super efficient but it does transfer a good deal of heat.


Nice! If and when you get to the project, take a few pics if you could so we could see how you did it!

1999 F350 Dually with 7.3 Diesel
2000 Bigfoot 10.6 Camper

jimh406
Explorer III
Explorer III
My house propane system runs at around 170. You need several finned radiators and a circulating pump. They are good heat but warm up rooms slow.

'10 Ford F-450, 6.4, 4.30, 4x4, 14,500 GVWR, '06 Host Rainer 950 DS, Torklift Talon tiedowns, Glow Steps, and Fastguns. Bilstein 4600s, Firestone Bags, Toyo M655 Gs, Curt front hitch, Energy Suspension bump stops.

NRA Life Member, CCA Life Member

toddb
Explorer
Explorer
I built a hydronic system in my old toy hauler. I started out using the water heater and then switched to a stand alone atwood water heater filled with glycol. It worked amazingly well, camped often to freezing and it maintained 65 in the trailer with a 50% duty cycle. The output was 140*, was really quiet, and didn't dry out the air in the trailer.

I'm currently collecting parts to utilize the water heater in the TC. Using the water in the tank is a bad idea, the anode crude plugs everything up. My plan is to pull the water heater and wrap a coil around it, topsflo circulation pump and 120mm fan/pc radiator. We use a use a similar setup at work to cool compressor heads, not super efficient but it does transfer a good deal of heat.

Chris_Bryant
Explorer II
Explorer II
Hydronic systems run at a much hotter temperature than water heaters for a reason, and there are no stainless tanks- aluminum, which is two alloys sandwiched together, the interior alloy being more sacrificial, or steel, which is porcelain lined. Either tank cutting and welding would be problematic.
-- Chris Bryant

adamis
Nomad II
Nomad II
JD5150 wrote:
I have worked around air to water heat exchangers most of my life. Hot air from engine exhaust blowing on a stainless or copper coil to heat water at 600 psi around 2 gallons or more a minute.

The idea you have most likely will not work. Someone mentioned that a 12 gallon RV water heater is around 12,000 btu. So lets say a 6 gallon one is 6,000 btu. By the time you use air flow/fan to blow the heat you will be down to 3,000 btu or less. The fan will cool the air some so there will be some loss of heat there from fan picking up cooler air and blowing through the radiator coil.

I just started looking at the Truma Combi eco plus. I'm still studying it to see how much juice it will take to run in electric and gas mode. I want to run it off solar and a 200 amp hour lithium battery pack plus gas if needed. It will do both at the same time


The lower BTU output actually works to my advantage in this scenario. An Atwood 8 Gallon water heater is 8,800 BTUs, an Atwood Furnace is 35,000 BTUs. I don't need 35,000 BTUs constantly, there is a cycle time involved or I will be cooked out of the camper. Having a constant 8,800 BTUs burning with a lower fan speed and lower overall heat level but over a longer running time can have the equivalent effect as a blast furnace running for shorter periods of time.

1999 F350 Dually with 7.3 Diesel
2000 Bigfoot 10.6 Camper

JD5150
Explorer
Explorer
I have worked around air to water heat exchangers most of my life. Hot air from engine exhaust blowing on a stainless or copper coil to heat water at 600 psi around 2 gallons or more a minute.

The idea you have most likely will not work. Someone mentioned that a 12 gallon RV water heater is around 12,000 btu. So lets say a 6 gallon one is 6,000 btu. By the time you use air flow/fan to blow the heat you will be down to 3,000 btu or less. The fan will cool the air some so there will be some loss of heat there from fan picking up cooler air and blowing through the radiator coil.

I just started looking at the Truma Combi eco plus. I'm still studying it to see how much juice it will take to run in electric and gas mode. I want to run it off solar and a 200 amp hour lithium battery pack plus gas if needed. It will do both at the same time