TT plugged in at home?

Xpd77
Explorer
Explorer
I currently have an Arctic Fox truck camper with an 13.5k btu AC unit. When I'm at home I can plug it in to a 110 outlet and still run the AC and some lights and Fridge. It is a 30amp unit.

I'm getting ready to purchase a travel trailer and it may be 50amp and have a 15k btu AC unit. Will I still be able to plug this in at home on 110? At the very lease I want to run the AC.
2012 F350 SRW Diesel. 2014 Arctic Fox 811. Torklift tiedowns, Fast Guns, and Stable Loads.
27 REPLIES 27

Xpd77
Explorer
Explorer
Thanks everyone for your replies. This was very helpful.
2012 F350 SRW Diesel. 2014 Arctic Fox 811. Torklift tiedowns, Fast Guns, and Stable Loads.

MERVer
Explorer
Explorer
We had an rv box installed at our home. It has a 50,30,20 amp receptacles on a 50 amp breaker. The 20 amp has it's own breaker. Since we were going to have this done we also had a cable box mounted and a water line run next to the RV box... a little over kill maybe but it's just like being at the camp ground minus the sewage hook up.
Mbagley

westend
Explorer
Explorer
SoundGuy wrote:
westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.


To be fair I did answer the OP's question directly in my first post back on Page 1 of this discussion ...

"No. Even in your current situation running a single 13,500 BTU A/C on a 15 amp drop you should be running only the A/C and nothing else. Attempting to run a 15,000 BTU A/C will only worsen the situation.

Can't get much clearer than that. :R
Yeah, OK.
'03 F-250 4x4 CC
'71 Starcraft Wanderstar -- The Cowboy/Hilton

JWRoberts
Explorer
Explorer
Nearly all outdoor receptacles are rated for 20 Amps so yes you can run your AC. Just obtain the necessary adapters. You cannot simply replace a 20A outlet with a 30A outlet. The wiring will have to be replaced or added to.

AmericalVette
Explorer
Explorer
SoundGuy wrote:
westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.


To be fair I did answer the OP's question directly in my first post back on Page 1 of this discussion ...

"No. Even in your current situation running a single 13,500 BTU A/C on a 15 amp drop you should be running only the A/C and nothing else. Attempting to run a 15,000 BTU A/C will only worsen the situation.

Can't get much clearer than that. :R


LOL! That cost me a beer!
Times fun when you're having flies!

SoundGuy
Explorer
Explorer
westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.


To be fair I did answer the OP's question directly in my first post back on Page 1 of this discussion ...

"No. Even in your current situation running a single 13,500 BTU A/C on a 15 amp drop you should be running only the A/C and nothing else. Attempting to run a 15,000 BTU A/C will only worsen the situation.

Can't get much clearer than that. :R
2012 Silverado 1500 Crew Cab
2014 Coachmen Freedom Express 192RBS
2003 Fleetwood Yuma * 2008 K-Z Spree 240BH-LX
2007 TrailCruiser C21RBH * 2000 Fleetwood Santa Fe
1998 Jayco 10UD * 1969 Coleman CT380

Old-Biscuit
Explorer III
Explorer III
Our 5vr is 50A
We parked it next to house and lived in it for 3 months while selling house
Plugged into 15A outlet
Ran 15K A/C, converter and TV ....no breaker trips, no low voltage, no issues

Fridge, water heater on propane

Occasionally used microwave but had to shut down A/C first

Yes you can do it with good line voltage, isolated 15A circuit (nothing but trailer on it) and good adapters/connections.
Is it time for your medication or mine?


2007 DODGE 3500 QC SRW 5.9L CTD In-Bed 'quiet gen'
2007 HitchHiker II 32.5 UKTG 2000W Xantex Inverter
US NAVY------USS Decatur DDG31

westend
Explorer
Explorer
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.

IMO, it's risky to run these high amperage devices on an unknown rated circuit. In most cases the RV owner will be connected into a garage circuit and those can vary by standards at that location and age of house. In my area, an unfinished garage will have 20 amp GFCI protected branch circuits and hopefully, will be separated from other house receptacles. That isn't always the case. If the garage is finished in the interior, 15 amp circuits are allowed. Another intrinsic installation method is that a builder may pull 20 amp wiring throughout the garage but will install 15 amp receptacles to save time and money. I see many of these installations.

An owner should be mindful of exactly what he has regarding the circuit he wishes to use to power the RV. I'd suggest to the OP that he should establish a 50 amp receptacle as close as possible to his new TT. This can be complex as new AWG 6 needs to be pulled back to the load center in the house but will be less risk than trying to run a 15K BTU A/C through an unknown branch circuit. The price of A/C replacement would be more than the 50 receptacle installation.

FWIW, my TT has 50 amp service. I installed a 50 amp receptacle in the garage. Since I had previously installed a subpanel for a welder with 75 amp service, it was easy to add an additional breaker and pull wire for a dedicated 50 amp receptacle for the TT.

Good luck to the OP and hopefully, this discussion helps out with his questions.
'03 F-250 4x4 CC
'71 Starcraft Wanderstar -- The Cowboy/Hilton

daveyboy12
Explorer
Explorer
Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more


Two hots and a cot

SoundGuy
Explorer
Explorer
myredracer wrote:
Anyone attempting to run an AC unit on a 15 amp circuit or are occasionally or frequently doing this are not meeting the min. requirements specified by the AC manufacturer. The fact that you CAN get your AC unit to run does not mean that all is well.


SoundGuy wrote:
To suggest that a standard 13,500 BTU roof mount A/C cannot be successfully started and run by a 15 amp breaker protected circuit is simplistic nonsense.


myredracer wrote:
This also is incorrect. I'm an EE and I will bet my degree on it.


Sorry for your loss. :W

As you said yourself -"A Dometic AC unit with a voltage rating of 115V should be able to operate satisfactorily at 103.5 to 126.5 volts and without incurring damage.

Of interest here is that the two common EMS units shut power off at 102 volts (Surge Guard) and 104 volts (Progressive Industries). IMO, 102 volts is too low. The figure of 104 volts could very well be based on the minimum allow voltage under ANSI & NEC (104.4).
"

In my test today nominal unloaded source voltage was ~ 121.5 vac, lowest voltage when the compressor first ramped up to speed was ~ 108 vac and settled in at ~ 114 vac with no other loads on the circuit and as such was nowhere near causing my Progressive EMS-HW30C from shutting down power to the trailer. As I recall, LRA for my particular Dometic Brisk II is ~ 65 amps or just 4.3x the breaker's nominal 15 amp rating, a TM breaker that won't instantly trip until the surge load is 7x that rating, or 105 amps, explaining why it never trips running my 13.5K Dometic A/C.

MY bottom line, repeated - with a nominal unloaded source voltage of +/- 120 vac, reasonable cable length, and adequate cable gauge there's absolutely no reason one can't successfully start and run a 13,500 BTU A/C unit from a household 15 amp circuit provided there are no other loads running on that circuit at the same time.
2012 Silverado 1500 Crew Cab
2014 Coachmen Freedom Express 192RBS
2003 Fleetwood Yuma * 2008 K-Z Spree 240BH-LX
2007 TrailCruiser C21RBH * 2000 Fleetwood Santa Fe
1998 Jayco 10UD * 1969 Coleman CT380

myredracer
Explorer II
Explorer II
Dick_B wrote:
On another Forum it was determined that the startup current of a Dometic 15K A/C is 13.6 amps with a 2.8 amps run current. That would imply that you can run the 15K A/C off the 20 amp circuit; but don't push it with other `stuff' on the same circuit.


Sorry, but that is so incorrect. RV AC units are typically around 15 amps running and starting (momentary inrush) current (technical term is locked rotor amps) is around 5-6 times the running current. The data listed in this Duo-Therm by Dometic Instructions shows that for a 15K BTU unit, the running current is 15.4 amps and the starting current is 77.0 amps. These figures are for running at the equipment's normal operating voltage and for the Dometic units is 115 volts, not 120 volts.

Note that the MINIMUM specified wire size for all Dometic AC units (13.5 or 15K BTU) is #12 gauge and the specified breaker size is 20 amps. This is the same for other manufacturer's AC units as well. Again, note that this is for running at 115 volts (at the terminals on the unit itself). There is also a specified max. run of 24 feet of #12 wire. The breaker is sized independent of wire size to prevent nuisance tripping of the breaker when starting. Wire is sized to maintain appropriate voltage and to comply with code.

"Nominal" AC line voltage is N. America is standardized at 120 volts. Power Utility companies are all on an interconnected grid and voltage tolerance boundary has to comply with ANSI standard C84.1 and the permitted variation from 120 volts is +/- 5 percent. However, if you include the voltage drop allowed by the NEC for a customer's premises, the permitted total variation allowed is + 6 percent and minus 13 percent. At the worst case scenario of a 13 perent, the voltage at the point of use on a customer's premise can be 104.4 volts and still comply with all codes and standards. The figure of 104.4 volts allows for voltage drop in a customer's wiring system up to the point of use. Pacific Gas and Electric has a very good explanation here.

If voltage at a CG is down to 104.4 volts, you have no code or standard you can point your finger at to blame the CG. However, if the voltage is indeed that low, it can in the majority of cases, have been higher because the NEC does not adequately provide for the quantity of 50 amps RVs in use today plus it allows for substantial downsizing feeder cables on an overall total basis of 41 percent for more than 36 pedestals.

The voltage rating found on some equipment is not 120 volts. The reason for this is that a manufacturer assumes and takes into account that the equipment will normally be operating at less than 120 volts. Equipment is also required to be able to run at +/- 10 percent of it's rated voltage. There will be a NEMA standard that covers this and the PG&E info. above makes mention of this. Motorized equipment in particular can have rated voltages less than 120 such as 110, 115 & 117 volts. A Dometic AC unit with a voltage rating of 115V should be able to operate satisfactorily at 103.5 to 126.5 volts and without incurring damage.

Of interest here is that the two common EMS units shut power off at 102 volts (Surge Guard) and 104 volts (Progressive Industries). IMO, 102 volts is too low. The figure of 104 volts could very well be based on the minimum allow voltage under ANSI & NEC (104.4). On this basis alone, I would not buy a Surge Guard EMS.

Anyone attempting to run an AC unit on a 15 amp circuit or are occasionally or frequently doing this are not meeting the min. requirements specified by the AC manufacturer. The fact that you CAN get your AC unit to run does not mean that all is well.

SoundGuy wrote:

To suggest that a standard 13,500 BTU roof mount A/C cannot be successfully started and run by a 15 amp breaker protected circuit is simplistic nonsense.


This also is incorrect. I'm an EE and I will bet my degree on it. Damage to an AC unit is not necessarily instantaneous. It can be cumulative over time. If you are running an AC unit on a 15 amp circuit, you are likely reducing it's life. Looking at the Dometic data, the normal running current at 115 volts for a 15K unit is 15.4 amps and for a 13.5K unit ranges from 13.5 to 14.6 amps (depending on model no.). By code (CEC or NEC), the min. wire size just for one AC unit running (and no other loads in the RV) would require a 20 amp circuit (by applying the 80 percent safety factor). On top of an AC unit's running current, you have to add any other running loads and at a min. can have the converter/charger and fridge drawing a few amps.

One thing that is unique to AC units is that they draw more current as the voltage goes down compared to just about anything else (resistive loads like say a heater, toaster or coffee maker and motors). And for those loads that have outputs that do go down as voltage goes down, their output drops as the square of the voltage and at 104 volts for example, output would be 69 percent of the rating at it's listed operating voltage of 120 volts nominal.

Say you are running just a 13.5K or 15K AC and no other loads and the voltage goes down, you will definitely be overloading the wire and exceeding the required breaker size. At some point as the voltage goes down, the unit's current will be high enough at starting to trip a breaker. It get's complicated to predict with other loads running at the same time. To an AC unit's required breaker size, you would typically add the running current of everything else. But with current of the AC going up when voltage goes down, there is no manufacturer's data available with which you can use to do a calc.

It is important to understand that an AC unit draws much more current during the initial startup of a few cycles or so of up to around 5-6 times the running current. In the case of a Dometic 15K unit, you are looking at 77.0 amps (5.7 times running current). So here you would have a 15 amp breaker and #14 wire at home trying to support 77 amps at startup. The result is a very high momentary voltage drop. If you do manage to get your AC unit running, every time it starts up, it suffers some degree of damage. It may not significant at each start up event, but over time it is cumulative and you can significantly reduce the life of an AC unit. Now, if the voltage is low and the running current is high, the starting current will be much higher than at 115 volts. This is one reason why an AC may start and seem to be running okay but will not restart.

Some homes will only have a 15 amp breaker and #14 wire. As well, a 15 amp recept. can have other loads connected on the same circuit. In the US, houses now have a 20 amp breaker and #12 wire feeding multiple recepts. and you *may* have a better chance of getting an AC unit to start and run satisfactorily. Receptacles on a 20 amp circuit use a "T-slot_ configuration that will accept a 15 amp or 20 amp plug so if you see a T-slot recept., it will be supplied by a 20 amp breaker and wire. At some point down the road your AC unit can fail and you will be left wondering how the heck it happened. I have looked and looked and have not been able to find data showing current draw versus voltage for RV AC units but it is an accepted fact that the current does go up with dropping voltage. Well pumps are one example where wire size can be increased to allow for the distance from the panel to the well and down to a submersible pump (can be hundreds of feet down) so that it will reliably start every time and so that damage will not be caused to it.

Another thing of interest is that 30 to 15 amp adapters are only rated at 15 amps and will be CSA listed as such. With just an AC unit running and everything else off inside an RV, the adapter will be operating over it's rating. So if voltage drops and you also have other loads running, the adapter can really be over-taxed. Add plugging in with a live circuit all the time (which damages plug and recept. contact surfaces), you have a recipe for damaging the adapter and causing a meltdown. The puck style adapters are the worst for heating up as they have a short path for heat to be transferred compared to a pigtail adapter.

Bottom line is that if you want your AC unit to run at home satisfactorily all the time, do not want adapters and extension cords to melt down and don't want to cause damage to the AC unit, don't plug into a 15 amp circuit/receptacle, don't use a 15 amp rated adapter and make sure the wire size (house panel to recept. on house and from the receptacle to the panel inside an RV is adequately sized. I'm not sure off-hand if and any 30/15 adapters have a 20 amp rating on the plug end, but if you have a T-slot receptacle at home you could make up your own adapter.

SoundGuy
Explorer
Explorer
RoyB wrote:
You will need these adapters to plug your 50AMP Shore Power Cable into 120VAC 15/20A Receptacle..





Your second illustration is incorrect as that looks like a 30 amp RV male connector to a 30 amp female twist lock connector. What the OP really needs for powering a rig wired with 50 amp main service is a 50 amp Female > 30 amp Male dogbone which he can then plug into that first dogbone you've illustrated, allowing him to draw from a 15 / 20 amp source.
2012 Silverado 1500 Crew Cab
2014 Coachmen Freedom Express 192RBS
2003 Fleetwood Yuma * 2008 K-Z Spree 240BH-LX
2007 TrailCruiser C21RBH * 2000 Fleetwood Santa Fe
1998 Jayco 10UD * 1969 Coleman CT380

pasusan
Explorer
Explorer
SoundGuy wrote:
Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more


Not as simple as that as success depends greatly on the ability of the circuit in question to provide voltage within the specified norms and to not suffer excess voltage drop under load due to excessive cable length and/or inadequate cable gauge. One must also factor in the breaker tripping time which for a typical 15 amp / 20 amp TM (thermal magnetic) breaker will allow up to 7 times surge voltage before causing an instant trip, ergo the reason an A/C's LRA (Locked Rotor Amp) rating that can easily be 65 amps isn't normally a factor.

I keep our trailer here at the house during the camping season plugged into a 15 amp drop in the workshop (here in Canada 20 amp is not a standard as it often is in the US). That 15 amp drop is fed from the house breaker box with an estimated 60' of 14 gauge Romex ... from there I have 25' of 10 gauge main service cable feeding the trailer. Ambient outside temperature both outside and inside the camper as I write this is ~ 85F or ~30C. With the trailer plugged into my workshop 15 amp source and everything in the trailer switched off, including the converter, unloaded source voltage reads ~ 121.5 vac. When I turned on the A/C fan voltage dropped a couple of volts, when I then turned on the A/C compressor voltage momentarily dropped to ~ 108 vac then quickly recovered to ~ 114.5 vac with a current draw reading on my Progressive EMS (which reads just to the volt) ranging from 12 to 13 amps. As A/C compressor head pressure began to increase voltage gradually dropped another volt to ~ 113.5 vac and current reading on my EMS reads 14 amps (again just to a unit value). It's now been running for a 1/2 hour just fine off this 15 amp circuit and would continue to run the rest of the day until I turn it off. :B
I agree with this. Our TT is stored in an old barn with electrical service installed in the 1950s. We don't run the A/C because we can see the voltage drop big time on our EMS. We want our A/C to last. 😉

Susan & Ben [2004 Roadtrek 170]
href="https://sites.google.com/view/pasusan-trips/home" target="_blank">Trip Pics

SoundGuy
Explorer
Explorer
Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more


Not as simple as that as success depends greatly on the ability of the circuit in question to provide voltage within the specified norms and to not suffer excess voltage drop under load due to excessive cable length and/or inadequate cable gauge. One must also factor in the breaker tripping time which for a typical 15 amp / 20 amp TM (thermal magnetic) breaker will allow up to 7 times surge voltage before causing an instant trip, ergo the reason an A/C's LRA (Locked Rotor Amp) rating that can easily be 65 amps isn't normally a factor.

I keep our trailer here at the house during the camping season plugged into a 15 amp drop in the workshop (here in Canada 20 amp is not a standard as it often is in the US). That 15 amp drop is fed from the house breaker box with an estimated 60' of 14 gauge Romex ... from there I have 25' of 10 gauge main service cable feeding the trailer. Ambient outside temperature both outside and inside the camper as I write this is ~ 85F or ~30C. With the trailer plugged into my workshop 15 amp source and everything in the trailer switched off, including the converter, unloaded source voltage reads ~ 121.5 vac. When I turned on the A/C fan voltage dropped a couple of volts, when I then turned on the A/C compressor voltage momentarily dropped to ~ 108 vac then quickly recovered to ~ 114.5 vac with a current draw reading on my Progressive EMS (which reads just to the volt) ranging from 12 to 13 amps. As A/C compressor head pressure began to increase voltage gradually dropped another volt to ~ 113.5 vac and current reading on my EMS reads 14 amps (again just to a unit value). It's now been running for a 1/2 hour just fine off this 15 amp circuit and would continue to run the rest of the day until I turn it off. :B
2012 Silverado 1500 Crew Cab
2014 Coachmen Freedom Express 192RBS
2003 Fleetwood Yuma * 2008 K-Z Spree 240BH-LX
2007 TrailCruiser C21RBH * 2000 Fleetwood Santa Fe
1998 Jayco 10UD * 1969 Coleman CT380