SoundGuy wrote:Yeah, OK.westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.
To be fair I did answer the OP's question directly in my first post back on Page 1 of this discussion ...
"No. Even in your current situation running a single 13,500 BTU A/C on a 15 amp drop you should be running only the A/C and nothing else. Attempting to run a 15,000 BTU A/C will only worsen the situation.
Can't get much clearer than that. :R
โAug-08-2016 05:02 PM
โAug-08-2016 02:52 PM
SoundGuy wrote:westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.
To be fair I did answer the OP's question directly in my first post back on Page 1 of this discussion ...
"No. Even in your current situation running a single 13,500 BTU A/C on a 15 amp drop you should be running only the A/C and nothing else. Attempting to run a 15,000 BTU A/C will only worsen the situation.
Can't get much clearer than that. :R
โAug-08-2016 12:59 PM
westend wrote:
Both of the above posts offer an accurate assessment of the workings of an RV A/C unit and the electrical requirements. Unfortunately, they are centered around running a 13.5K BTU unit. The OP is asking about a 15K BTU unit and his household branch circuit.
โAug-08-2016 12:29 PM
โAug-08-2016 11:13 AM
โAug-08-2016 10:42 AM
Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more
โAug-08-2016 10:26 AM
myredracer wrote:
Anyone attempting to run an AC unit on a 15 amp circuit or are occasionally or frequently doing this are not meeting the min. requirements specified by the AC manufacturer. The fact that you CAN get your AC unit to run does not mean that all is well.
SoundGuy wrote:
To suggest that a standard 13,500 BTU roof mount A/C cannot be successfully started and run by a 15 amp breaker protected circuit is simplistic nonsense.
myredracer wrote:
This also is incorrect. I'm an EE and I will bet my degree on it.
โAug-08-2016 09:45 AM
Dick_B wrote:
On another Forum it was determined that the startup current of a Dometic 15K A/C is 13.6 amps with a 2.8 amps run current. That would imply that you can run the 15K A/C off the 20 amp circuit; but don't push it with other `stuff' on the same circuit.
SoundGuy wrote:
To suggest that a standard 13,500 BTU roof mount A/C cannot be successfully started and run by a 15 amp breaker protected circuit is simplistic nonsense.
โAug-08-2016 09:11 AM
RoyB wrote:
You will need these adapters to plug your 50AMP Shore Power Cable into 120VAC 15/20A Receptacle..
โAug-08-2016 09:07 AM
SoundGuy wrote:I agree with this. Our TT is stored in an old barn with electrical service installed in the 1950s. We don't run the A/C because we can see the voltage drop big time on our EMS. We want our A/C to last. ๐Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more
Not as simple as that as success depends greatly on the ability of the circuit in question to provide voltage within the specified norms and to not suffer excess voltage drop under load due to excessive cable length and/or inadequate cable gauge. One must also factor in the breaker tripping time which for a typical 15 amp / 20 amp TM (thermal magnetic) breaker will allow up to 7 times surge voltage before causing an instant trip, ergo the reason an A/C's LRA (Locked Rotor Amp) rating that can easily be 65 amps isn't normally a factor.
I keep our trailer here at the house during the camping season plugged into a 15 amp drop in the workshop (here in Canada 20 amp is not a standard as it often is in the US). That 15 amp drop is fed from the house breaker box with an estimated 60' of 14 gauge Romex ... from there I have 25' of 10 gauge main service cable feeding the trailer. Ambient outside temperature both outside and inside the camper as I write this is ~ 85F or ~30C. With the trailer plugged into my workshop 15 amp source and everything in the trailer switched off, including the converter, unloaded source voltage reads ~ 121.5 vac. When I turned on the A/C fan voltage dropped a couple of volts, when I then turned on the A/C compressor voltage momentarily dropped to ~ 108 vac then quickly recovered to ~ 114.5 vac with a current draw reading on my Progressive EMS (which reads just to the volt) ranging from 12 to 13 amps. As A/C compressor head pressure began to increase voltage gradually dropped another volt to ~ 113.5 vac and current reading on my EMS reads 14 amps (again just to a unit value). It's now been running for a 1/2 hour just fine off this 15 amp circuit and would continue to run the rest of the day until I turn it off. :B
โAug-08-2016 08:49 AM
Terryallan wrote:
Fact is. IF it pulls too many amps it will trip the breaker. then you know you need more