dougrainer wrote:
1. Year and MODEL of the RVP HP
2. Do you get ANY air volume inside?
3. Was the Compressor running before you changed the Capacitors?
4. Is this a ducted unit?
5. Icing----Lines or the Evaporator? Doug
โJun-18-2016 11:35 AM
โJun-18-2016 08:39 AM
โJun-18-2016 06:10 AM
โJun-18-2016 05:23 AM
โJun-18-2016 04:59 AM
โJun-18-2016 04:03 AM
โJun-18-2016 03:21 AM
โJun-18-2016 02:19 AM
smkettner wrote:
For icing up:
Assuming you have a wall thermostat you should have a freeze sensor that needs to be right up on the evaporator. These are notorious for falling away due to poor installation.
Secondly while you have removed all the interior trim to find the freeze sensor, check that the divider that separates the air in and air out plenum is well placed and sealed to prevent recirculating of chilled air.
But I find it odd you say it is iced up and the tech says a needs a new unit. Are you sure it is iced up? Usually they will blow cold air for at least 20 minutes before the ice interferes with cooling.