BigFly10 wrote:
- I opened the A/C breaker for the converter and plugged the trailer shore power cord directly into the inverter. Interestingly, this works great. I can run the microwave over and over again without tripping the inverter GFCI.
โAug-13-2013 08:54 AM
โAug-13-2013 07:38 AM
john&bet wrote:
One point that none have touched on is that you may be overloading your gfi. Is it a 20amp gfi or a 15 amp? There was a time that the school of thought was not to plug a microwave into a gfi even in your home. Not sure if that still holds true. I wonder why your inverter even has GFI output on it for your application?
โAug-13-2013 07:34 AM
westend wrote:
I'm betting that your ground wire for the DC system is not up to the task. Using an 8 AWG ground,with 4 batteries and an inverter trying to pull +1500 watts, the inverter is seeing a low voltage condition. Your use of an extension cord may be just enough to allow some capacitance to overcome the inverter's bad feelings about the situation.
The frame ground from the inverter is just as MrWizard has stated, a protection and interference device, not part of the power profile.
โAug-13-2013 01:40 AM
โAug-13-2013 01:10 AM
โAug-12-2013 11:16 PM
VintageRacer wrote:
Make sure your sub panel does not have neutral bonded to ground. It must separate neutral and ground, the transfer switch must switch both neutral and hot to the inverter, which must bond neutral and ground. Neutral is always bonded to ground at one point only, and that is the source of the power. Remember that GFCI - ground fault circuit interrupter - is a bit of a misnomer. The device does nothing with ground at all and can be installed in a circuit that does not have ground (such is code-allowed for protecting old 2 conductor wiring in old houses). It does trip if there is any difference between the current flowing in the hot conductor and the current flowing in the neutral conductor. Having neutral bonded in two places can create such a difference.
Brian
โAug-12-2013 09:22 PM
shooted wrote:
Can you provide a wiring diagram of your installation? It appears to be a problem isolated to the sub panel or ATS.
Edit, on second thought, the problem is probably at the ATS, or between the ATS and inverter. I would verify wiring at the ATS paying special attention to proper/correct connection from the inverter. I suspect a wire assembly defect between ATS and inverter.
โAug-12-2013 01:55 PM
โAug-12-2013 01:08 PM
โAug-12-2013 12:54 PM
โJul-31-2013 08:36 AM
โJul-31-2013 07:49 AM
BFL13 wrote:
My inverter's instructions make a big point to NEVER run the chassis ground lug wire over to the inverter's own neg input terminal (which goes back to the neg grounded battery) but run it straight to the frame.
Even though there is a path through the frame back through the battery (also frame grounded) the direct inverter frame ground seems to be ok under the rules.
I got lost in the OP ๐ but there may be a variation on this no-no there.
The purpose of the inverter's chassis to frame wire grounding is to reduce radio and TV interference. The inverter will run just fine without the chassis ground being connected.
An intermittent GFCI issue may be due to a loose connection somewhere?
โJul-30-2013 04:47 PM
โJul-30-2013 03:23 PM