notruffinit wrote:
OK. So I shut off all the breakers and it will still trip the GFCI. So I guess the problem must be between my hardwired Surge Guard and the Main Breaker box (which is about 2 feet of wire)? I installed the SurgeGuard myself. I know that the common and the ground are separated. My coach is wired for 50 amp with a 50 amp Surge Guard, but I have only 1 AC unit so I almost never plug into 50 amp. I prefer to use the much smaller 30 amp cord. Anything there that I am missing?
Old-Biscuit wrote:
When you turned all the breakers off did that include the Main Breaker(s) also
Turn ALL breakers OFF and then see if GFCI still trips. If it does...problem is between pedestal and Main Panel
Bad adapter, bad cord, bad connections in cord, bad wiring.......
IF it doesn't trip then turn Main Breaker(s) ON and repeat.
Then one breaker at a time.
Bobbo wrote:
Somewhere in your RV there is a NEUTRAL to GROUND short. It could be anywhere.
Disconnect the RV from all power. Remove all NEUTRAL wires from the buss bar in the breaker box. Plug back in. If it trips, the problem is between the Surge Guard and the breaker box.
If it doesn't blow, disconnect, reattach one NEUTRAL wire, reconnect. If it blows, that is the circuit with the problem. If it doesn't blow, repeat process till it blows.
When it blows, trace that NEUTRAL to see where it connects to ground. It could be in a stripped/pinched/punctured wire, an outlet, an appliance, anywhere.
Jim Cindy wrote:
We see the same thing if we plug into any, not just campround, outlet that is GFI protected. I would be interested in an explanation too. I was previously told that it was because the RV does not have a ground to earth that the GFI is looking for.