MrRchitty wrote:
If you deep discharge, I think you'll have a problem. With daily maintenance, it should not be an issue. You will pull almost if not a little more than 1000 watts.
โAug-03-2011 12:33 PM
Angus_NB wrote:
After reading 40+ pages of the 171 in this thread I was nearly convinced that a trip to Costco was in my future.
The following has me concerned though;Searching_Ut wrote:
...
Biggest issue I have is that the little champion just doesn't like my WFCO 55 amp converter in my TT. The power factor on the converter is .67, which is murder on the generator. If I let my two type 24 batteries drop down to about half charge, the converter draws right around 700 watts when I first plug the trailer in to the generator. With that much of a reactive load the overload trips right around 700 to 720 watts, so half the time when I first plug the trailer in, it kicks the overload. Trying other less reactive loads I can get up to 1600 watts, sometimes slightly higher. The other issue with the converter in the TT is that the generator tends hunt a fair bit throttle wise when trying to power the TT with nothing else on, which is something it doesn't do nearly so much with other loads. On an intersting side note, I borrowed a little 2 cycle 1000 watt generator which is only rated for 800 continuous and it works great with the power convertor in the TT.
...
I have a WFCO WF-8955PEC in my trailer. My main purpose for getting a generator is to recharge the two Group 24 batteries.
Is there something I can do to verify that the CPE 2000i is going to work for me?
I don't mind buying one and trying it out but I don't want to find out it can't charge my batteries when I am 100s of miles from home.
โAug-03-2011 12:30 PM
#40Fan wrote:PrivatePilot wrote:
As for my situation, I don't want to go into details on how I'm being taken care of, but suffice to say I'm happy.
What? Why not? I am sure that we would all like to know what they are doing to remedy your situation. Without facts we are only left to speculate.
โAug-03-2011 12:24 PM
Old & Slow wrote:PrivatePilot wrote:bradyk wrote:
Dennis maybe can add to the burping issue on our gennys, Seems pretty common out there that no one has a magic answer for. I didn't notice it so much but the wife pointed out to me last weekend. I wouldn't put it in the deal breaker category but is it something that is going to get worse or maybe an internal component going to fail down the road. Maybe Dennis can read many of those posts and throw us some ideas.
It's nearing the "it's going back to the store" category for me, depending on how it behaves this weekend at a outdoor jamboree we are attending. It'll probably be running about 16 hours a day for 3 days - if at the end it's still burping and wandering it's idle all over the map I think mine will be going back in the box and back to Costco.
I love the little Champ when it's running right, but this burping and wandering throttle issue *IS* a deal breaker for me.
What a difference a day makes. From a minus to a 'possible' plus for Champion.
The CEO Mr. Dennis Trine with (CPE) must have known all along about the problems with the Champion 2000i. With the coming of the fix, just like that. Bingo. What the fix for the leaking and burping is *is* will be one of the most watched for posts, I think in the history of RV.Net.
I continue to be in the hunt for a nice priced Inverter Generator that has many and mostly good reports.
โAug-03-2011 09:20 AM
โAug-03-2011 09:05 AM
Searching_Ut wrote:
...
Biggest issue I have is that the little champion just doesn't like my WFCO 55 amp converter in my TT. The power factor on the converter is .67, which is murder on the generator. If I let my two type 24 batteries drop down to about half charge, the converter draws right around 700 watts when I first plug the trailer in to the generator. With that much of a reactive load the overload trips right around 700 to 720 watts, so half the time when I first plug the trailer in, it kicks the overload. Trying other less reactive loads I can get up to 1600 watts, sometimes slightly higher. The other issue with the converter in the TT is that the generator tends hunt a fair bit throttle wise when trying to power the TT with nothing else on, which is something it doesn't do nearly so much with other loads. On an intersting side note, I borrowed a little 2 cycle 1000 watt generator which is only rated for 800 continuous and it works great with the power convertor in the TT.
...
โAug-01-2011 09:10 PM
โJul-31-2011 07:09 PM
โJul-31-2011 11:27 AM
โJul-31-2011 10:28 AM
MrRchitty wrote:
I traveled to the Outer Banks, NC just the other day and boondocked in a church parking lot for a few hours. Because of the heat and humidity that night, the twins powered the AC unit only and while laying in bed, the power went out.
Randall
โJul-30-2011 07:12 PM
orionpaxx wrote:
hey guys,
what do you find is the easiest why to clean the spark arrestor? where do you get replacements?
all is still going great with my pair powering the coffee wagon.
Jay
โJul-30-2011 06:35 PM
orionpaxx wrote:
hey guys,
what do you find is the easiest why to clean the spark arrestor? where do you get replacements?
all is still going great with my pair powering the coffee wagon.
Jay