โMay-20-2015 04:32 AM
โMay-20-2015 01:31 PM
Chris Bryant wrote:
You are always going to have a small leak- the solenoid valves on appliances do not seal perfectly- ANSI standards call for less than 240 cc/hr leakage as being acceptable.
The reason for using a manometer is so you can quantify the leak to make certain is is within allowable limits- something that you cannot do using the changeover indicator.
โMay-20-2015 01:20 PM
โMay-20-2015 12:28 PM
โMay-20-2015 10:38 AM
โMay-20-2015 10:02 AM
derh20 wrote:
i don't know if the is helpful or not, but i had a leak once and it turned out the person that filled my tank did not tightened that screw fully that is used to get the air out of the tank before filling. i can't remember the name of that screw.
โMay-20-2015 09:38 AM
JimK-NY wrote:
Thanks. If I understand the manometer will show the drop in pressure but not the volume rate of leakage. Anyway it sounds like there will always be some leaking due to the valves on the furnace and HW heater. I guess I should be able to see those leaks with soap testing. I will give it another try. I was thinking that the leak was at the regulator.
โMay-20-2015 08:55 AM
โMay-20-2015 08:25 AM
โMay-20-2015 08:12 AM
In a way it does show the rate- no drop from an 8" water column movement in 3 minutes means the leak is small enough to be inconsequential (some states call for up to 15 minutes- the time I use for testing). The trouble with watching the changeover indicator is that you have a volume of high pressure LP in the pigtails, which can keep the pressure up even with a leak.
โMay-20-2015 08:04 AM
โMay-20-2015 07:51 AM
โMay-20-2015 07:12 AM
โMay-20-2015 06:56 AM
โMay-20-2015 06:34 AM