theoldwizard1 wrote:2oldman wrote:A very wise decision, but it makes charging and powering 12VDC item more of a challenge.
Some of us have gone to 24 or 48 volts to lessen line loss and use thinner, more flexible wire.
GordonThree wrote:
An inexpensive DC-DC converter provides 12v for small loads like pump, lights, etc.
โJan-21-2018 06:36 AM
2oldman wrote:
Some of us have gone to 24 or 48 volts to lessen line loss and use thinner, more flexible wire.
โJan-21-2018 05:23 AM
โJan-21-2018 05:06 AM
opnspaces wrote:
As far as the distance, the horizontal run is not that far, more like 3 feet if I went straight from the batteries through the front wall of the trailer.
SoundGuy wrote:
I wouldn't do that - if the inverter is mounted in the front pass through storage compartment go down through the floor, along the underside of the A-frame, and up to the batteries.
brulaz wrote:
Oh I dunno. That's what I did. ๐ As straight a path to the batteries as possible, carefully caulked.
But my front wall consists of a cap + space + interior wall.
โJan-21-2018 04:39 AM
SoundGuy wrote:opnspaces wrote:
As far as the distance, the horizontal run is not that far, more like 3 feet if I went straight from the batteries through the front wall of the trailer. But that seems like a leak point so I was picturing going down from the batteries, back to the trailer then up through the floor. Now that I have a better idea how much distance affects wire gauge, voltage drop, and price; I'm going to reconsider the path to see how much I can shorten it.
I wouldn't do that - if the inverter is mounted in the front pass through storage compartment go down through the floor, along the underside of the A-frame, and up to the batteries. In my case that turned out to be 6', meaning 12' of cable for positive & negative, both 4 gauge for my maximum ever load of 70 amps. You sure don't want to go through the trailer's front wall - instead increase the gauge of the cable to whatever may be necessary to meet your load & distance requirements.
โJan-20-2018 06:39 PM
โJan-20-2018 06:28 PM
opnspaces wrote:
As far as the distance, the horizontal run is not that far, more like 3 feet if I went straight from the batteries through the front wall of the trailer. But that seems like a leak point so I was picturing going down from the batteries, back to the trailer then up through the floor. Now that I have a better idea how much distance affects wire gauge, voltage drop, and price; I'm going to reconsider the path to see how much I can shorten it.
โJan-20-2018 06:03 PM
SoundGuy wrote:
The question though in your case is, aside from heavy wiring necessary to make the most of a 2000 watt inverter what do you intend to use to power the inverter, 'cause a single battery sure isn't going to do it? :h
โJan-20-2018 05:46 PM
pianotuna wrote:
opnspaces,
Zamp is pricey compared to some other inverters. Unless you have it already I'd suggest something else.
The inverter needs to be as close as humanly possible to the battery bank without being in the same compartment.
My wire run is about four feet--and that is LONG for a 3k unit.
โJan-20-2018 05:44 PM
MEXICOWANDERER wrote:
Here's a real world tip about voltage drop influence...
Coffeemaker 950 watts
24 oz brew 55F water
At 120vac one minute fifteen seconds
At 100vac two minutes thirty (five?) seconds
Microwave. 8oz russet potato
Seven minutes
Eleven and a half minutes
" Need 4x #10 to make #4 "
Double wire drop three sizes 2x10 9-8-7 (seven gauge)
Works with AWG. SAE wire gauge doesn't cut it...
โJan-20-2018 05:37 PM
GordonThree wrote:
10 gauge is speaker wire, not suitable for an inverter. Where did 10 gauge come from?
Why is the inverter being installed so far from the batteries?
โJan-20-2018 05:30 PM
time2roll wrote:
If the tag says 13 amps load you can count on close to 130 amps from the 12 volt battery. (amps x10)
Best to stay away from parallel wires unless the inverter has dual input terminals. Get the right stuff. I posted a link above.
As far as equivalent wire you need to convert to circular mils to add the cross section of copper. But again try to stay away from parallel.
Cross section area is on this ampacity chart:
http://www.genuinedealz.com/voltage-drop-calculator
Need 4x #10 to make #4
โJan-20-2018 05:23 PM
GordonThree wrote:
Gotta love AGM for their flexibility. My setup sounds sounds similar to BFL13's ... I have my 2800w inverter snuggled with four G31 12v AGM under a heavily reinforced dinette seat. More than four years now, no issues with anything. It's a bit untidy, I left slack in my 4/0 welding cable to be able to pull out the inverter without disconnecting the batteries, for troubleshooting or whatever.
Load test, run the 13.5 A/C and the microwave, the inverter heats up a bit, that fan gets going good but the battery cables stay nice and cool while carrying almost 300 amps.
โJan-20-2018 03:52 PM
โJan-20-2018 02:46 PM