dahkota wrote:BFL13 wrote:
You can get the inverter to not alarm off until at a lower SOC by using shorter/fatter wires between it and the battery bank.
I see a 0.8v drop while running a load that pulls 90 amps from the battery bank of four wet 6s. This means I can be at 12.2v to start and it will stay above the 11.0v alarm point. (Allows for the initial drop to 11.4 and then some for decline while load is running)
Ah - I have my alarm set at 11.9. The 90 or so amps my pot pulls causes a .5V drop with AGMs. Can I really run the volts that low without damaging anything?
โOct-26-2015 04:31 PM
โOct-26-2015 04:25 PM
BFL13 wrote:
You can get the inverter to not alarm off until at a lower SOC by using shorter/fatter wires between it and the battery bank.
I see a 0.8v drop while running a load that pulls 90 amps from the battery bank of four wet 6s. This means I can be at 12.2v to start and it will stay above the 11.0v alarm point. (Allows for the initial drop to 11.4 and then some for decline while load is running)
โOct-26-2015 02:22 PM
โOct-26-2015 01:57 PM
GordonThree wrote:
whole house is a big cash outlay, but is so nice...
โOct-26-2015 01:32 PM
โOct-26-2015 12:52 PM
jeffwhite wrote:
I was not sure what I was going to do about this, as I have decent access to the back of this partucular outlet (I think, if I pull the microwave),but getting from the inverter to the outlet might me sketchy. What is the transfer switch you are talking about? jeff